Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

CM4250- ECC21 and PM5000 (PM5330)

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • CM4250- ECC21 and PM5000 (PM5330)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
engineer_langfo
engineer_langfo
Explorer

Posted: ‎2016-02-01 03:05 PM

0 Likes
4
2244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-01 03:05 PM

CM4250- ECC21 and PM5000 (PM5330)

Can the ECC21 on an existing CM4250/CM3350 support RS485 communications to the PM5000 series?

Customer has existing CM4250 with ECC21 integrated to PME.   Would like to add one PM5330 in the electrical room and use the existing ECC21 on the meter as a gateway to the new meter.   Is this supported?

Tags (3)
  • Tags:
  • cm4000
  • ecc21
  • pm5000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
sesa50168
sesa50168 Leader
Leader

Posted: ‎2016-02-01 03:20 PM

0 Likes
2
2200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-01 03:20 PM

Hi Eric -

The ECC21 card has Ethernet gateway functionality, and supports Modbus.  The PM5330 is a Modbus meter, so yes, you can use the CM4250 + ECC21 to gateway the PM5330 to Ethernet.  You just need to follow the wiring instructions to install the correct jumpers in the ECC21 terminal block, since the ECC21 can handle either 2 wire or 4 wire RS485.

Reply
engineer_langfo
engineer_langfo
Explorer

Posted: ‎2016-02-01 04:31 PM

0 Likes
1
2200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-01 04:31 PM

It is that easy?  And there is no special configuration in the CM4250 /ECC21. 

Wire properly.

Simply identify the PM5330 meter in PME Management Console as if it was another meter like the PM820?. 

Done?

Reply
sesa50168
sesa50168 Leader
Leader

Posted: ‎2016-02-02 12:03 PM

0 Likes
0
2200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-02 12:03 PM

OK - there is the step in which you access the ECC21 web page and add the Modbus address of the PM5330.  But that's a simple, quick process.  The ECC card does not care what the device is - it just needs to know the Modbus address of the device.  Once you've added the device on the ECC card, you set up the CM4250 as a gateway in Management Console and add the PM5330 as another meter to the system.  It is easy.  If there are any questions/issues, Tech Support can walk the customer through it.

Reply
michael_franz
michael_franz
Mentor

Posted: ‎2017-06-23 06:58 AM

0 Likes
0
2200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-23 06:58 AM

Eric:

The ECC is like any other gateway.  Match RS485 parameters.  Easy as Pi.  You can also use a 4 - 2 wire converter if going all two wire is not practical.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore