Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Sanjeet_Sahota
Lieutenant Lieutenant
Lieutenant

Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Currently most generator battery monitoring solutions requires a V4 voltage input for capturing the battery voltage waveform.  Since the waveform capture on the meter does not remove DC from the voltage input signal, this can be compared against known good reference waveforms in software to develop reports on the differences as seen in our user manuals below.

 

1..png2.png

 

Originally limited to the ION7650, ION7550, and ION9000, there now exists an alternate solution using the AIO module (METSEPM89M0024) to expand this functionality to the PM8000 and ION7400 (or even on the ION9000 if V4 is already in use).

 

The Analog Input modules can be set to “Voltage” mode to monitor up to 4 battery sources per module (up to a maximum of 16) on a single meter!  Each analogue input is sampled every ½ cycle (120Hz for 60Hz systems) and are rated up to 30VDC solution

 

This provides an array of benefits:

  • Battery is electrically isolated from meter voltage measurement inputs to simplify installation
  • Each AIO module contains 4 analog inputs and each meter can support up to 4 modules
  • Higher accuracy, true DC voltage measurement; 0.3% full scale vs current un-calibrated method
  • No need for an additional digital input to initiate data capture as a set-point module can be used


Setting up the AIO module is simple to allow for basic high-speed ( ½ cycle) logging of the V Batt

 

3.png

 

This can be further explored to do more using the set-point module to trigger pre-event and post-event data that can be translated into “waveform-like” data. 


See the example below used by one of our colleagues to monitor the starter on his motorcycle.  He was able to generate a graph from the data logged in the data-recorder using the burst logging as found in the pre/post-event data capture:

 

4.png5.png

 

 

Do more with your meter!


Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
0
1238

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Hello Jeffrey,

 

Currently, the EPSS report will look in the waveofrmlog2 table in the database for the V4 waveform. With the above configuration, the logging is done in a data recorder that logs the data to Datalog2. So correct, currently not something that can be done with the report as it is currently designed. 

 

Will this always be the case: unknown, are there workarounds: possibly but I personally do not know them.

 

Regards,

Charles

 

P.S. Note that the ION9000 meter does have a V4 connection, this setup is more for PM8000 or ION, but could be done with ION9000 if additional sources were desired.

L4 Prime for Advanced metering and Utilities

See Answer In Context

7 Replies 7
TewfikBoudiba
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
1332

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Hello @Sanjeet_Sahota,

 

Useful, can you share the ION file ?

Stay efficient with EcoStruxurePower
Aminadra
Commander Commander
Commander

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

is it possible to use this with the PME reports?  it was possible with the 7650 

JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
0
1289

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

You should definitely post the ION Framework for this above. Only makes sense.

jan_opsteyn
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
1276

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Is this  possibel to measure the true RMS DC voltage. We tried or with pm8000 and AI but the flinke tree RMS meter is giving different voltage....

 

We need  to measure on red circle

below 0-35V Dc

image002.png

 

Charles_Murison
Picard Picard
Picard
0 Likes
2
1261

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

The data recorded by the meter is not in a waveform format as the report would expect. It is possible to trend this data using Diagrams/Vista or exporting the data to Excel.

L4 Prime for Advanced metering and Utilities
sesa28787_bridg
Ensign Ensign
Ensign
0 Likes
1
1243

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Charles are you saying this would not be a alternate option, instead of using the V4 connection for EPSS Battery Monitoring waveform report? 

Charles_Murison
Picard Picard
Picard
0 Likes
0
1239

Re: Battery Monitoring through the AIO Module for ION9000, ION7400, PM8000

Hello Jeffrey,

 

Currently, the EPSS report will look in the waveofrmlog2 table in the database for the V4 waveform. With the above configuration, the logging is done in a data recorder that logs the data to Datalog2. So correct, currently not something that can be done with the report as it is currently designed. 

 

Will this always be the case: unknown, are there workarounds: possibly but I personally do not know them.

 

Regards,

Charles

 

P.S. Note that the ION9000 meter does have a V4 connection, this setup is more for PM8000 or ION, but could be done with ION9000 if additional sources were desired.

L4 Prime for Advanced metering and Utilities