Hello Community,
question about the parallel connection, in the installation manual it is just mentioned the modbus serial through RJ45 connector pin-out, but the manual doesn't mention anything about the parallel connection pin-out, so is it T-568A to T-568A or T-568A to T-568B???
Looking forward to your answer,
BR
Link copied. Please paste this link to share this article on your social media post.
Hello Horacio,
T-568B to T-568B works.
We strongly recommend to use quality wires provided by SE.
BRs
Yan
Link copied. Please paste this link to share this article on your social media post.