Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AccuSine PCS+/PCSn: Can we install PCS+ and PCSn in the same parallel system?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • AccuSine PCS+/PCSn: Can we install PCS+ and PCSn in the same parallel system?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
NguyenMon
NguyenMon
Explorer

Posted: ‎2020-03-05 08:47 PM . Last Modified: ‎2020-12-02 03:31 AM

2 Likes
3
3624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-05 08:47 PM

AccuSine PCS+/PCSn: Can we install PCS+ and PCSn in the same parallel system?

Hi everyone,

Have a nice day.

 

We have a customer who had installed 2 PCS+ units for mitigating 3-phase harmonics before and now they want to install 2 PCSn units to mitigate neutral harmonic. Can we install 2 PCSn units to the 2 PCS+ system in parallel? I demonstrate the system we're about to build in the picture below. Please look into it and give me some directions if anything needs correcting or notes in configuration.

 

Thank you in advance,

Nguyen

 

PCS_Sys.PNG

 

Labels
  • Labels:
  • Power Quality
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2020-03-10 09:37 PM

1 Like
1
3612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-10 09:37 PM

@NguyenMon 

 

Here are our direction on your query, in addition to that,  i would appreciate if you can share below information in details.

What is the application? 

What is the customer name?

In which country you are planning for this set up?

 

Our Directions for PCSn and PCS+ operating in parallel on the same bus

 

 

 

The two AccuSine systems, PCS+ and PCSn will have to operate as independent system:

 

  • The PCS+ will be programmed to for PF and harmonic correction, however we will disable (turn OFF) harmonic mitigation for all the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …)
  • The PCSn will only be programmed for harmonic mitigation and we will only enable (Turn ON) the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …).

 

              We can use the existing CT’s for current sensing for the PCSn, simply daisy chain the CT signal       from the  PCS+ to the PCSn master unit, has shown in green.  In the drawing below, Consider the    third Master unit to be the first PCSn master unit (if multiple PCSn units are required).

 

There won’t be any Can bus communication between the PCS+ and the PCSn.

However, we will have Can Bus communication between each PCS+ or PCSn if multiple units of each kind is required.

Having a common breaker means no redundancy in maintenance or in case of a breaker trip.

Regarding neutral cable size , this would depend on how much Neutral harmonic is required, so I’d say size the neutral cable based on the neutral harmonic output/compensation.

 

BR

Arun

Arunprasad

See Answer In Context

Attachments
Reply
Replies 3
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2020-03-08 10:35 PM

1 Like
0
3619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-08 10:35 PM

@NguyenMon 

Hi

 

I need to check with my offer team, i will get back to you on this topic.

 

BR

Arun

Arunprasad
Reply
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2020-03-10 09:37 PM

1 Like
1
3612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-10 09:37 PM

@NguyenMon 

 

Here are our direction on your query, in addition to that,  i would appreciate if you can share below information in details.

What is the application? 

What is the customer name?

In which country you are planning for this set up?

 

Our Directions for PCSn and PCS+ operating in parallel on the same bus

 

 

 

The two AccuSine systems, PCS+ and PCSn will have to operate as independent system:

 

  • The PCS+ will be programmed to for PF and harmonic correction, however we will disable (turn OFF) harmonic mitigation for all the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …)
  • The PCSn will only be programmed for harmonic mitigation and we will only enable (Turn ON) the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …).

 

              We can use the existing CT’s for current sensing for the PCSn, simply daisy chain the CT signal       from the  PCS+ to the PCSn master unit, has shown in green.  In the drawing below, Consider the    third Master unit to be the first PCSn master unit (if multiple PCSn units are required).

 

There won’t be any Can bus communication between the PCS+ and the PCSn.

However, we will have Can Bus communication between each PCS+ or PCSn if multiple units of each kind is required.

Having a common breaker means no redundancy in maintenance or in case of a breaker trip.

Regarding neutral cable size , this would depend on how much Neutral harmonic is required, so I’d say size the neutral cable based on the neutral harmonic output/compensation.

 

BR

Arun

Arunprasad
Attachments
Reply
NguyenMon
NguyenMon
Explorer

Posted: ‎2020-03-22 08:08 PM

1 Like
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-22 08:08 PM

Hi @Arunprasad ,

Have a nice day.

 

Thank you for your help.

We're planning to install this at outgoing low voltage for Noi Bai airport in Vietnam.
I'm sorry for wrong information i gave you in the topic. The purpose of this set up is to mitigate the 3rd harmonic which existing system (PCS+ system) couldn't mitigate efficiently.
So with this change, can your notes be usable now? Please give me notes if anything need changing.

I'm sorry for the inconvenience.

 

BR,

Nguyen

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore