AccuSine PCS+/PCSn: Can we install PCS+ and PCSn in the same parallel system?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • AccuSine PCS+/PCSn: Can we install PCS+ and PCSn in the same parallel system?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
NguyenMon
Lieutenant | EcoXpert Master NguyenMon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-03-05 08:47 PM . Last Modified: ‎2020-12-02 03:31 AM

2 Likes
3
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-05 08:47 PM

AccuSine PCS+/PCSn: Can we install PCS+ and PCSn in the same parallel system?

Hi everyone,

Have a nice day.

 

We have a customer who had installed 2 PCS+ units for mitigating 3-phase harmonics before and now they want to install 2 PCSn units to mitigate neutral harmonic. Can we install 2 PCSn units to the 2 PCS+ system in parallel? I demonstrate the system we're about to build in the picture below. Please look into it and give me some directions if anything needs correcting or notes in configuration.

 

Thank you in advance,

Nguyen

 

PCS_Sys.PNG

 

Labels
  • Labels:
  • Power Quality
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-03-10 09:37 PM

1 Like
1
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-10 09:37 PM

@NguyenMon 

 

Here are our direction on your query, in addition to that,  i would appreciate if you can share below information in details.

What is the application? 

What is the customer name?

In which country you are planning for this set up?

 

Our Directions for PCSn and PCS+ operating in parallel on the same bus

 

 

 

The two AccuSine systems, PCS+ and PCSn will have to operate as independent system:

 

  • The PCS+ will be programmed to for PF and harmonic correction, however we will disable (turn OFF) harmonic mitigation for all the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …)
  • The PCSn will only be programmed for harmonic mitigation and we will only enable (Turn ON) the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …).

 

              We can use the existing CT’s for current sensing for the PCSn, simply daisy chain the CT signal       from the  PCS+ to the PCSn master unit, has shown in green.  In the drawing below, Consider the    third Master unit to be the first PCSn master unit (if multiple PCSn units are required).

 

There won’t be any Can bus communication between the PCS+ and the PCSn.

However, we will have Can Bus communication between each PCS+ or PCSn if multiple units of each kind is required.

Having a common breaker means no redundancy in maintenance or in case of a breaker trip.

Regarding neutral cable size , this would depend on how much Neutral harmonic is required, so I’d say size the neutral cable based on the neutral harmonic output/compensation.

 

BR

Arun

Arunprasad

See Answer In Context

Attachments
Reply
Replies 3
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-03-08 10:35 PM

1 Like
0
2026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-08 10:35 PM

@NguyenMon 

Hi

 

I need to check with my offer team, i will get back to you on this topic.

 

BR

Arun

Arunprasad
Reply
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-03-10 09:37 PM

1 Like
1
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-10 09:37 PM

@NguyenMon 

 

Here are our direction on your query, in addition to that,  i would appreciate if you can share below information in details.

What is the application? 

What is the customer name?

In which country you are planning for this set up?

 

Our Directions for PCSn and PCS+ operating in parallel on the same bus

 

 

 

The two AccuSine systems, PCS+ and PCSn will have to operate as independent system:

 

  • The PCS+ will be programmed to for PF and harmonic correction, however we will disable (turn OFF) harmonic mitigation for all the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …)
  • The PCSn will only be programmed for harmonic mitigation and we will only enable (Turn ON) the zero sequence harmonics (3rd, 6th, 9th, 12th, 15th, …).

 

              We can use the existing CT’s for current sensing for the PCSn, simply daisy chain the CT signal       from the  PCS+ to the PCSn master unit, has shown in green.  In the drawing below, Consider the    third Master unit to be the first PCSn master unit (if multiple PCSn units are required).

 

There won’t be any Can bus communication between the PCS+ and the PCSn.

However, we will have Can Bus communication between each PCS+ or PCSn if multiple units of each kind is required.

Having a common breaker means no redundancy in maintenance or in case of a breaker trip.

Regarding neutral cable size , this would depend on how much Neutral harmonic is required, so I’d say size the neutral cable based on the neutral harmonic output/compensation.

 

BR

Arun

Arunprasad
Attachments
Reply
NguyenMon
Lieutenant | EcoXpert Master NguyenMon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-03-22 08:08 PM

1 Like
0
2007
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-22 08:08 PM

Hi @Arunprasad ,

Have a nice day.

 

Thank you for your help.

We're planning to install this at outgoing low voltage for Noi Bai airport in Vietnam.
I'm sorry for wrong information i gave you in the topic. The purpose of this set up is to mitigate the 3rd harmonic which existing system (PCS+ system) couldn't mitigate efficiently.
So with this change, can your notes be usable now? Please give me notes if anything need changing.

I'm sorry for the inconvenience.

 

BR,

Nguyen

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of