3P PowerTag for single phase load

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 3P PowerTag for single phase load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2022-12-27 07:27 AM

0 Likes
4
2009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-27 07:27 AM

3P PowerTag for single phase load

Hi All,

 

Is it possible to use F63 (3P+N, 1570) and F160 (3P+N, 1580) to measure single-phase load?

Do they need to be powered on with all voltage inputs X/Y/Z or can be powered with single voltage input X?

Thank you

3.pngScreenshot 2022-12-27 232157.png

Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-01-03 12:46 AM

0 Likes
0
1976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 12:46 AM

Hello,


Many remarks about your question:

 

  • For security reason, the installation of a 3ph PowerTag installed downstream to several 1Ph circuit breakers is forbidden because the physical separation of the 3 phases with the load is not insured when only the associated circuit breaker is switched off (risk of Power loop through the PowerTag itself (screenshot 1 extracted from the PowerTag catalog)
  • Regarding the gateway who gather data, all the measurements will not be relevant, (example: Average current which is the average of the 3 phase currents will not make sense if only one phase is wired.)
  • Regarding the upper SE on-premises softwares : Native drivers of (PME, PO) will not  propose relevant value for 3 phases  average measurements.
  • Regarding SE cloud application (EEH, FE…):  these kind of upper systems  will not be able to manage properly the PowerTag   so it is not possible  for this type of architecture.
  • Obviously only a customized development in the upper client (BMS, PLC, SCADA) to collect only the relevant measurement shall be advised
  • Regarding the power, it is possible to supply  only between 1 phase and neutral or between two phases for the two models. However for F63 A9MEM1570, the two not used phase voltage picking must be wired in a terminal block (even if not used)  for security reasons. In my opinion it makes sense to prefer to use one or several A9MEM1560 (1ph +N) instead A9MEM1570.

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Attachments
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-01-03 02:28 AM

0 Likes
0
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 02:28 AM

Hello @Stuart_Cheng , 

 

Important question: what is the voltage of your load ?

  1. 230 Vac ? In this case, why not using A9MEM1560 ? Load current higher than 63 amps ? 
  2. 400 Vac ? In this case check my answer below.

By design you can power supply F63 and F160 between N+Ph1. But as mentioned by Thierry, F63 unused phases must be connected somewhere in your enclosure (PE) => but in this case, this could lead to earth leakage (DDR trip) in case of internal failure of the PowerTag sensor (risk is very low, but never 0 especially if the PowerTag is not correctly wire to the breaker - true story).


You can also power supply the Powertag F63, F160 by connecting beween L1-L2, L2-L3, L3-L1 if you have a 1ph 400 Vac load. Same remark as above for the F63 voltage and neutral probes that are not connected to the breaker.

 

If you are using Panel Server or PowerTag Link as a gateway, following measurement will be pertinent:

  • Voltage P-N or P-P (depending on your load)
  • Phase current (A, B or C).
  • Total Power
  • Total Energy

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-01-03 07:52 AM

0 Likes
0
1964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 07:52 AM

I complete the 2 previous posts concerning PowerTag voltage picking connection after discussion with R&D team.

  • It is not advised to leave the PowerTag voltage picking unconnected  or to connect to PE (as mentionned in the 2 previous posts). It is better to  fix a referential voltage by adding bridge between phase voltage picking even if the phase is not used for power measurement ( in attachment an example to count energy for a one phase load)

 

  • Whatever the wiring, you must also check that the real voltage is in the rated voltage range defined in the catalog. (Higher voltage will damage the PowerTag) 

A9MEM1570:  Max Phase to Neutral voltage between 220 and 240VAC +/-20%  / Max Phase to Phase voltage between 380 and 415VAC +/-20%

A9MEM1580:  Max Phase to Neutral voltage between 100 and 277VAC +/-20%  / Max Phase to Phase voltage between 173 and 480 VAC +/-20%

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Attachments
Reply
Replies 4
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-01-03 12:46 AM

0 Likes
0
1977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 12:46 AM

Hello,


Many remarks about your question:

 

  • For security reason, the installation of a 3ph PowerTag installed downstream to several 1Ph circuit breakers is forbidden because the physical separation of the 3 phases with the load is not insured when only the associated circuit breaker is switched off (risk of Power loop through the PowerTag itself (screenshot 1 extracted from the PowerTag catalog)
  • Regarding the gateway who gather data, all the measurements will not be relevant, (example: Average current which is the average of the 3 phase currents will not make sense if only one phase is wired.)
  • Regarding the upper SE on-premises softwares : Native drivers of (PME, PO) will not  propose relevant value for 3 phases  average measurements.
  • Regarding SE cloud application (EEH, FE…):  these kind of upper systems  will not be able to manage properly the PowerTag   so it is not possible  for this type of architecture.
  • Obviously only a customized development in the upper client (BMS, PLC, SCADA) to collect only the relevant measurement shall be advised
  • Regarding the power, it is possible to supply  only between 1 phase and neutral or between two phases for the two models. However for F63 A9MEM1570, the two not used phase voltage picking must be wired in a terminal block (even if not used)  for security reasons. In my opinion it makes sense to prefer to use one or several A9MEM1560 (1ph +N) instead A9MEM1570.

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Attachments
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-01-03 02:28 AM

0 Likes
0
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 02:28 AM

Hello @Stuart_Cheng , 

 

Important question: what is the voltage of your load ?

  1. 230 Vac ? In this case, why not using A9MEM1560 ? Load current higher than 63 amps ? 
  2. 400 Vac ? In this case check my answer below.

By design you can power supply F63 and F160 between N+Ph1. But as mentioned by Thierry, F63 unused phases must be connected somewhere in your enclosure (PE) => but in this case, this could lead to earth leakage (DDR trip) in case of internal failure of the PowerTag sensor (risk is very low, but never 0 especially if the PowerTag is not correctly wire to the breaker - true story).


You can also power supply the Powertag F63, F160 by connecting beween L1-L2, L2-L3, L3-L1 if you have a 1ph 400 Vac load. Same remark as above for the F63 voltage and neutral probes that are not connected to the breaker.

 

If you are using Panel Server or PowerTag Link as a gateway, following measurement will be pertinent:

  • Voltage P-N or P-P (depending on your load)
  • Phase current (A, B or C).
  • Total Power
  • Total Energy

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-01-03 07:52 AM

0 Likes
0
1965
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 07:52 AM

I complete the 2 previous posts concerning PowerTag voltage picking connection after discussion with R&D team.

  • It is not advised to leave the PowerTag voltage picking unconnected  or to connect to PE (as mentionned in the 2 previous posts). It is better to  fix a referential voltage by adding bridge between phase voltage picking even if the phase is not used for power measurement ( in attachment an example to count energy for a one phase load)

 

  • Whatever the wiring, you must also check that the real voltage is in the rated voltage range defined in the catalog. (Higher voltage will damage the PowerTag) 

A9MEM1570:  Max Phase to Neutral voltage between 220 and 240VAC +/-20%  / Max Phase to Phase voltage between 380 and 415VAC +/-20%

A9MEM1580:  Max Phase to Neutral voltage between 100 and 277VAC +/-20%  / Max Phase to Phase voltage between 173 and 480 VAC +/-20%

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Attachments
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2023-01-03 08:55 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-03 08:55 AM

Hi @Thierry_Baudard  and @Romain_Polette 

 

Thank you so much for the input.

 

The reason I asked this question is because of the supply chain issue. The delivery time of A9MEM 1560 is longer than A9MEM 1570, which is why we are considering an alternative way. For sure A9MEM1560 (1ph +N) is a better option for 1 ph load.

 

Your information is really helpful. I will check with the customer about the remarks you have mentioned.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of