Hi All,
Is it possible to use F63 (3P+N, 1570) and F160 (3P+N, 1580) to measure single-phase load?
Do they need to be powered on with all voltage inputs X/Y/Z or can be powered with single voltage input X?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Hello,
Many remarks about your question:
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Important question: what is the voltage of your load ?
By design you can power supply F63 and F160 between N+Ph1. But as mentioned by Thierry, F63 unused phases must be connected somewhere in your enclosure (PE) => but in this case, this could lead to earth leakage (DDR trip) in case of internal failure of the PowerTag sensor (risk is very low, but never 0 especially if the PowerTag is not correctly wire to the breaker - true story).
You can also power supply the Powertag F63, F160 by connecting beween L1-L2, L2-L3, L3-L1 if you have a 1ph 400 Vac load. Same remark as above for the F63 voltage and neutral probes that are not connected to the breaker.
If you are using Panel Server or PowerTag Link as a gateway, following measurement will be pertinent:
Regards,
Link copied. Please paste this link to share this article on your social media post.
I complete the 2 previous posts concerning PowerTag voltage picking connection after discussion with R&D team.
A9MEM1570: Max Phase to Neutral voltage between 220 and 240VAC +/-20% / Max Phase to Phase voltage between 380 and 415VAC +/-20%
A9MEM1580: Max Phase to Neutral voltage between 100 and 277VAC +/-20% / Max Phase to Phase voltage between 173 and 480 VAC +/-20%
Link copied. Please paste this link to share this article on your social media post.
Hello,
Many remarks about your question:
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Important question: what is the voltage of your load ?
By design you can power supply F63 and F160 between N+Ph1. But as mentioned by Thierry, F63 unused phases must be connected somewhere in your enclosure (PE) => but in this case, this could lead to earth leakage (DDR trip) in case of internal failure of the PowerTag sensor (risk is very low, but never 0 especially if the PowerTag is not correctly wire to the breaker - true story).
You can also power supply the Powertag F63, F160 by connecting beween L1-L2, L2-L3, L3-L1 if you have a 1ph 400 Vac load. Same remark as above for the F63 voltage and neutral probes that are not connected to the breaker.
If you are using Panel Server or PowerTag Link as a gateway, following measurement will be pertinent:
Regards,
Link copied. Please paste this link to share this article on your social media post.
I complete the 2 previous posts concerning PowerTag voltage picking connection after discussion with R&D team.
A9MEM1570: Max Phase to Neutral voltage between 220 and 240VAC +/-20% / Max Phase to Phase voltage between 380 and 415VAC +/-20%
A9MEM1580: Max Phase to Neutral voltage between 100 and 277VAC +/-20% / Max Phase to Phase voltage between 173 and 480 VAC +/-20%
Link copied. Please paste this link to share this article on your social media post.
Hi @Thierry_Baudard and @Romain_Polette
Thank you so much for the input.
The reason I asked this question is because of the supply chain issue. The delivery time of A9MEM 1560 is longer than A9MEM 1570, which is why we are considering an alternative way. For sure A9MEM1560 (1ph +N) is a better option for 1 ph load.
Your information is really helpful. I will check with the customer about the remarks you have mentioned.