Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Xenta Programmable Device is Offline in Vista but Online in LonMaker

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta Programmable Device is Offline in Vista but Online in LonMaker
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Anonymous user
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4181 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta Programmable Device is Offline in Vista but Online in LonMaker

Picard Product_Support
‎2018-09-07 12:49 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:24 PM

Issue

Xenta Programmable Device is Offline in Vista, but Online in LonMaker.

For LonWorks Devices refer to LonWorks Device is Offline in Vista but Online in LonMaker or NL220.

Product Line

TAC Vista

Environment

  • LonMaker, NL220
  • Vista Workstation
  • Xenta programmable controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B

Cause

In an LNS system, Xenta programmable controllers have different methods of communication to the LNS server and the Vista server.  Communication with the LNS server indicates the wiring is connected, the neuron ID is set correctly, but does not guarantee communication with the Vista server.  An online condition for Vista is dependent on Xenta Group bindings and network description files in the device and the Xenta Group Master being online.

Resolution

  1. Ensure that Vista Workstation is in Operating Mode vs. Engineering Mode.
  2. Refresh the Folders View - Highlight the root directory "TAC Vista" press "F5" or click the refresh icon.
  3. Ensure the device is physically Online in LonMaker even though the drawing displays as green.
    Check the status by right clicking on the device, select Properties.
    Commission Status should say "Current", and State should say "Online".
    Alternatively, right click on the device and select Manage / Test. 
    The state should read "configured online" if the device is online in LonMaker.
  4. Make sure that your Master Device in the corresponding Xenta Group in the System Plug-in is online.
    If the Master Device is online and displaying values, it is always necessary to download the application and parameters to the Xenta group after adding a new device.
    The entire Xenta Group must know there is a new device for proper communication to occur. 
    Download the applications and parameters to the entire group in the TAC System Plug-In.
  5. If all the above is true and there is still no data then use Verifying Xenta Group Bindings in an LNS system to verify that the Xenta Group Bindings are correct.
    If not, in the Vista system plug-in, click on the LNS Network tab choose Create Group Bindings and click Yes on the Resynchronize drawing to database (Fix-up Drawing).
  6. Ensure the Xenta Group name is less than 20 characters without any spaces.
    Note: Channel names can contain spaces (NL220) but still must stay under the 20 character limit. 
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 1905
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore