Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Unable to Create a backup in DBCreate

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to Create a backup in DBCreate
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Roger_Bently
    Roger_Bently
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1699 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to Create a backup in DBCreate

Picard Product_Support
‎2018-09-07 04:01 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:35 PM

Issue

Unable to create a backup of an I/NET Seven Database using DBCreate, gets a backup failed error.

Product Line

TAC INET

Environment

Windows XP, Windows Vista OS, with SQL 2000, 2003 and 2005.

Cause

Functionality of the host pc and the database seems to be inconsistent.

Resolution

Option 1:

  1. Stop all of the SQL Services (SQL Server, SQL Agent, SQL Distributed Coordinator)
  2. Copy INetDb.mdf and INetDb_log.ldf to an alternate locations (located in C:\Program Files\Microsoft SQL Server\MSSQL.1\MSSQL\Data)
  3. Restart all SQL Services.
  4. Launch DBCreate and remove the existing I/NET Seven Database.
  5. Create a new I/NET Seven Database.
  6. Stop all of the SQL Services (SQL Server, SQL Agent, SQL Distributed Coordinator)
  7. Copy the saved INetDb.mdf and INetDb_log.ldf over the newly created files.
  8. Restart all SQL Services.
  9. Launch DBCreate and attempt a backup.

Option 2 (If Option 1 does not work)

  1. Stop all of the SQL Services (SQL Server, SQL Agent, SQL Distributed Coordinator)
  2. Copy INetDb.mdf and INetDb_log.ldf to an alternate locations (located in C:\Program Files\Microsoft SQL Server\MSSQL.1\MSSQL\Data)
  3. Uninstall and Reinstall I/NET Seven.
  4. Stop all of the SQL Services (SQL Server, SQL Agent, SQL Distributed Coordinator)
  5. Copy the saved INetDb.mdf and INetDb_log.ldf over the newly created files.
  6. Restart all SQL Services.
  7. Launch DBCreate and attempt a backup.

Refer to How to Troubleshoot on DBCreate for more issues about DBCreate.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 4307
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore