EcoStruxure WebReports Installation Errors (1001 while importing report pack)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EcoStruxure WebReports Installation Errors (1001 while importing report pack)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4784 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure WebReports Installation Errors (1001 while importing report pack)

Picard Product_Support
‎2018-09-11 05:11 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:40 AM

Issue

Getting an Error 1001 near the end of the EcoStruxure WebReports Installation

Reports not functional from WebReports

Product Line

EcoStruxure Building Operation

Environment

  • Web Reports
  • SQL 2008 R2
  • Windows Server 2008
  • Windows Server 2012

Cause

This error is caused when the WebReports installer is unable to reach SQL Server Reporting Services to configure the WebReports Interface

Resolution

After a failed install of WebReports you will need to follow the general workflow:
 
  1. Clean of the Pieces of the failed install. Use the uninstall process listed in the WebReports Reference Guide or Uninstall Process for Web Reports.
  2. Correct all possible causes of the failed install
  3. Verify that you can connect to the ES using http from the Reports Server PC
  4. Verify that you can connect to http://localhost/Reports_SQLInstanceName 
  5. Re-install WebReports.

NOTE: You may be able to correct the issue without having to remove and re-install WebReports.

Possible Issue: The Microsoft Reporting Service SQL databases are not registered

  1. Check through SQL Management Studio that the 2 databases "ReportServer$instance" and "ReportServer$instanceTempDB" are registered. If not, the SBO Web Reports installed have nowhere to place the report pack files.
  2. If they are not there, you need to add them through "Reporting Services Configuration Manager". Click "Database" and then "Change Database". Here you can chose to create new databases.

Possible Issue: Insufficient User Access

  1. Log out of Windows and Log back in using a PC admin account. The account logged in for the installation should have full access to Windows and be a DB admin in the SQL Server.
  2. Set the User Account Control Settings to Never notify.

Possible Issue: PC Configured as a Domain Server

  1. In the Server Manager, check that the IIS Role is configured and that there are no Domain Roles assigned to this PC

Possible Issue: Another Application is using a Required SQL function

  1. Uninstall any application which use SQL on this PC. (The Enterprise Server does not Use SQL)
  2. As a Best Practice, the Reports Server should be installed on its own, dedicated PC.

Possible Issue: Incorrect Version of SQL Server or Windows Server

  1. Check the Reports Server Specification Sheet for your build and verify that you are on the Correct Version of Windows and SQL.

Possible Issue: Secure Connection Level set too high

  1. This issue typically also results in not being able to log into http://localhost/Reports_SQLExpress.
  2. Log into the Reporting Agent Configuration Manager Application
  3. Click on the Report Manager URL on the left-hand column
  4. Click on the HTTP URL
  5. This will give you the correct URL for your installation of SQL
  6. If this fails, browse to C:\ProgramFiles\Microsoft SQL Server\MSRS10_50.SQLEXPRESS\Reporting Services\ReportServer (this may vary based on SQL Installation)  
  7. Modify the CONFIG file "rsreportserver"
  8. Change the Secure ConnectionLevel to "0"
  9. Save the file and attempt to log into http://localhost/Reports_SQLExpress again.
  10. For more details on this property see: http://technet.microsoft.com/en-us/library/aa179559(v=sql.80).aspx

Possible Issue: .NET Framework is not operating correctly.

  1. Download the correct version of .NET framework for your version of EBO (The correct required version can be found on WebHelp Reports Server under EcoStruxure Building Operation Software Requirements)
  2. Run the installer in "Repair" mode

Possible Issue: The Windows account "appuser" is not created because the default password does not meet password policy requirements

  1. Temporarily disable password policy on the server and try reinstalling.
  2. For clarification of the use of 'appuser', refer to the following article, Report Server "appuser" clarification 
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 13598
  • RobertAndriolo24
  • SharlinaRenwall22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore