Node reset messages are received at regular time intervals after a BAS 2800+ to Sigma upgrade
  • Node reset messages are received at regular time intervals after a BAS 2800+ to Sigma upgrade
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-07 02:31 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:23 AM
Node reset messages are received at the Sigma server on a regular basis.
Satchwell Sigma
  • Sigma software - all releases.
  • Sigma firmware - all versions.
Messages designed to be sent to a server are being sent to a device node.
The BAS 2800+ system allows Controllers and Terminals to have the same numbers allocated. In Sigma this is not possible as all device numbers are unique. Should a reference to a terminal accidently be left in a controller configuration, then the controller may send messages to this device number, the receiving controller will then reset.
There are two ways to locate the source of the messages being sent to the resetting controller, they are:
  1. Use SigView to display all of the object data for a controller, and then search the data for the node number of the resetting controller. You will be looking for entries such as T(resetting node number).
OR
  1. Disconnect the controller from the network, and then connect a laptop, configured with the controller IP Address, and running WireShark to record all network messages.
  2. Allow WireShark to run for a period greater than the time between controller node resets.
  3. Filter the WireShark messages to review only messages sent to the IP Address of the resetting node. Check what the source IP address of these messages is, and then use SigView to review this controllers data.
A typical Wireshark display is shown below, in this case the trace is filtered on the "Source" IP Address.
For more information on using WireShark, please review Using WireShark to analyse communications on an Ethernet network.
  • Satchwell BAS & Sigma
Tags (2)
  • 4939
  • start
This is a heading