Using WireShark to analyse communications on an Ethernet network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using WireShark to analyse communications on an Ethernet network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8978 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using WireShark to analyse communications on an Ethernet network

Picard Product_Support
‎2018-09-07 11:51 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM

Issue

General use of the Wireshark program.

Product Line

Access Expert, Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Pelco, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista

Environment

Ethernet Networks

Cause

General Information on using WireShark.

Resolution

Wireshark is an Ethernet packet analysis programme, Which can be downloaded from:

  • Latest version available from Wireshark
  • Locally stored version 1.0.9

Installing Wireshark

  1. If necessary, unzip the WireShark executable file to a suitable location on the PC/Laptop you wish the programme to be installed on.
  2. Run the executable file and follow the on-screen instructions.

Rules for capturing LAN traffic using Wireshark:

Do not use a switch or router to connect the LAN capture PC to the network as these will filter important network activity that you will need to see. You will want to capture everything that is passing over the network at the point of concern. Usually, this means tapping into the ethernet at the Controller or controllers, that is having an issue.

midBit-Technologies-LLC-10-100 is an example of a device that can be used to easily tap into the network to take the capture.

The monitoring PC must see all traffic from the controller's point of view.

The monitoring PC can be connected in either two ways:

  1. Connected to the network at the controller
  2. The customers IT department can mirror all the network traffic from the controllers port to another port the PC can be connected to.

If connected to the network at the controllers, the connection must be made through a true ethernet hub. A hub will not selectively filter important network traffic as a switch or a router will do.

More information on what a "true ethernet hub" can be found at http://wiki.wireshark.org/HubReference

There are however some switches that feature port mirroring, please see How to Configure a NETGEAR Prosafe Plus Switch for Mirroring.

If connected to a mirrored port, the port must mirror 100% of the network traffic to and from the controller. No filtering should be done. Once a complete capture file has been obtained it can be filtered after the fact using WireShark or EtherReal.

Using Wireshark

  1. Run WireShark
  2. Start a trace by choosing the "Capture" menu and then select "Interfaces"
  3. Choose the appropriate interface. Generally, this can be identified by its IP Address, but if not, then the packets increasing are an indication.
  4. Press the "Start" button. The trace will start and will be similar to the following screenshot.
  5. After an appropriate time, the trace can be stopped by selecting "Capture" menu and "Stop"
  6. To save the capture file, choose "File" menu and "Save As".
Labels (10)
Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
Attachments
wireshark-setup-1.0.9.zip
Tags (4)
  • Find more articles tagged with:
  • 5133
  • PeterLarsen22
  • PeterLarsen24
  • wiretap
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.