Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Ordering more Newron NL220 credits

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Ordering more Newron NL220 credits
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2923 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Ordering more Newron NL220 credits

Picard Product_Support
‎2018-09-07 06:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:39 PM

Issue

How to order more NL credits in order to commission more devices.

If the following message displays when opening a NL220 database, then more credits will need to be purchased soon.
" BEWARE: less than 20 credits are available on this machine. If you need to install more than 20 device please order the amount of needed credits as soon as possible. Do you want to ask for new credits?"

Product Line

TAC IA Series, TAC Vista

Environment

  • NL220
  • LNS

Cause

There are two types of credits:

  1. Product specific credits like LonMaker and NL credits
  2. LNS credits

     

Echelon LNS

LNS credits are assigned to the PC and when they reach zero, the LNS Server license goes into deficit mode. After 14 days the deficit mode will expire, at which time no LNS tools will be able to be used on that PC. To reverse the lockout, enough LNS credits must be ordered to cover the deficit and any additional nodes that need to be commissioned. Backing up, sharing, and restoring LNS databases can sometimes corrupt these LNS credits, which then prohibits you from launching any LNS plug-ins. For more help with corrupt LNS credits see Corrupted LNS Credits.

Echelon LonMaker

LonMaker credits are assigned to the PC. Both LNS and LonMaker credits are required, however when commissioning devices in LonMaker, LonMaker credits are consumed but LNS credits are not. Even though LNS credits are not consumed in LonMaker they are still necessary because certain LNS applications (i.e. TAC Vista System Plug-in) require them to operate.

Newron NL220

Each time a node is commissioned in NL220 it requires a NL credit and a LNS credit. NL credits are assigned to the NL220 dongle and can be used on other PCs in "MOVED" mode. LNS credits are also necessary in NL220 to operate certain LNS applications such as the TAC Vista System Plug-in.

 

To order more Echelon LNS credits see Ordering more LNS credits.

To order more Echelon LonMaker credits see Ordering more Echelon LonMaker credits.

Resolution

When working in NL220, it is wise to maintain a higher level of LNS credits than NL credits to help avoid locking out the LNS server license.

  • To check the amount of NL credits remaining go to Start > All Programs > NL Suite > NLCreditsGenerator and look for Remaining NLCredits. The number of NL credits remaining can also be found at the bottom of the NL220 LonWorks Manager window with a project open.
  • To check the amount of LNS credits remaining on a PC go to Start > All Programs > Echelon LNS Utilities > LNS Server License Wizard and look for Credits Available. The number of LNS credits remaining can also be found at the bottom of the NL220 LonWorks Manager window with a project open.

 

To order more NL220 credits:

  1. Open the NLCreditsGenerator Utility that is installed with NL220. Go to Start > All Programs > NL Suite > NLCreditsGenerator > NLCreditsGenerator Utility.
  2. Enter the number of NL220 credits to be added  in the request area. Click Next.
  3. Click "Yes, this PC will be used for commissioning"
  4. Enter your name and contact details. Select "Copy to clipboard".
  5. Then either paste the information into notepad or in an email. Send the NL credit request to your local Schneider Electric Buildings Business order department  (NLCredits@buildings.schneider-electric.com).
  6. When you order has been processed by the local Schneider Electric Buildings Business order department you will receive an upgrade key.
  7. Open the NLCreditsGenerator Utility again. Go to Start > All Programs > NL Suite > NLCreditsGenerator > NLCreditsGenerator Utility.
  8. Click the Next button.
  9. Enter the key into the "Upgrade key" field of the credits generator.
  10. A message indicating you credits were added is then displayed.
     

Note: Once the request key has been generated, DO NOT commission or decommission any devices with the dongle until the upgrade key has been applied to the dongle. If devices are commissioned before then, the upgrade key will no longer be valid.

Labels (2)
Labels:
  • TAC IA Series
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4597
  • PeterLarsen24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore