Installing and configuring Vista OPC Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Installing and configuring Vista OPC Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • SESA116857
    SESA116857
  • Sacco
    Sacco
  • SESA128463
    SESA128463
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2889 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Installing and configuring Vista OPC Server

Picard Product_Support
‎2018-09-07 03:56 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:45 PM

Issue

What are the typical steps to install and configure Vista OPC Server?

Product Line

TAC Vista

Environment

  • Vista 5.1.x
  • Vista OPC Server 1.6.1

Cause

OPC Server can be used in many integration situations to provide data to other parties or bring third party data into the Vista front end.

Resolution

  1.  Install TAC Vista OPC Server 1.6.1 installation package
  2. Add a Windows Account for Vista OPC Server
    1. Start Computer Management
    2. In System Tools\Local Users and Groups\Users click New User
      1. Name the user OPC_Communication
      2. Provide a password
      3. Uncheck the User must change password at next logon checkbox
      4. Check User cannot change password checkbox
      5. Check Password never expires checkbox
      6. Click Create and Close.
    3. Add user to the Administrators group
  3. Configure Service
    1. In Services right click on TAC Vista OPC Server and click properties
      1. Ensure Startup type is Manual
      2. On Log On tab select This Account
      3. Browse to the local account OPC_Communication
      4. Provide the password in the Password and Confirm password fields
      5. Click OK
  4. Configuring DCOM
    1. Start Component Services
    2. Double click Component Services\Computers\My Computer\DCOM Config
    3. Locate the COM Server TAC Object Server OPC DA Services and select properties
      1. Click the Identity tab
      2. Select This User
      3. Select the local account OPC_Communication
      4. Provide the password in the Password and Confirm password fields
      5. Click OK
    4. Locate the COM Server TAC Object Server OPC AE Services and select properties
      1. Click the Identity tab
      2. Select This User
      3. Select the local account OPC_Communication
      4. Provide the password in the Password and Confirm password fields.
      5. Click OK
  5. Create a Vista User Account
    1. Start Vista Server
    2. Start Vista Workstation and Log In
    3. In the root TAC Vista folder create a new account (User - Vista or User - Windows Domain Group)
    4. Name the user TACOPC
    5. Modify the properties of the account
      1. Set the password
      2. Set an authority level that OPC Clients should use when accessing the OPC Server
      3. Set the Logout time to zero(0)
  6. Configure the Vista OPC Server Login
    1. Open TAC Vista OPC Server Setup (Program Files\Schneider Electric\TAC Vista OPC Server\Vista OPC Server Setup)
      1. Ensure the Retry connect period is 360 seconds.
      2. In the logon to TAC Vista Server click Login using the following Vista Account
      3. In the Username type TACOPC
      4. Type the password
      5. Click OK
      6. Confirm the change took place, if it is not refer to OPC server for TAC Vista will not keep the login settings in the TAC Vista OPC Server setup.
  7. Configuring Windows Firewall
    1. If Vista Server and OPC Server are on the same computer then no firewall exceptions are required. Consult the OPC Server manual (Chapter 4) for the firewall exceptions if using a separated OPC Server and Vista Server setup.
  8. Configuring OPC Client DCOM Settings
    1. If the OPC Client is on another computer then create a user account to match the one used by Vista OPC Server.
      1. Start Computer Management
      2. In System Tools\Local Users and Groups\Users click New User
        1. Name the user OPC_Communication
        2. Provide a password
        3. Uncheck the User must change password at next logon checkbox
        4. Check User cannot change password checkbox
        5. Check Password never expires checkbox
        6. Check Create and Close
    2. Configure Access Permissions
      1. Start Component Services on the Vista OPC Server computer under Administrative Tools
        1. In the Tree Structure right click on Component Services\Computers\My Computer and click properties
        2. Click the COM Security tab
        3. In Access Permissions click Edit Limits
          1. Click Add
          2. Select the local account OPC_Communication (EXAMPLE: W7USCNU1342VXXX\OPC_Communication)
          3. In the allow column select Local Access and Remote Access
          4. Click OK
        4. In Access Permissions click Edit Default
          1. Click Add
          2. Select the local account OPC_Communication
          3. In the allow column select Local Access and Remote Access
          4. Click OK
        5. In Launch and Activation Permissions click Edit Limits
          1. Click Add
          2. Select the local account OPC_Communication
          3. In the allow column select Local Launch, Remote Launch, Local Activation, and Remote Activation
          4. Click OK
        6. In Launch and Activation Permissions click Edit Default
          1. Click Add
          2. Select the local account OPC_Communication
          3. In the allow column select Local Launch, Remote Launch, Local Activation, and Remote Activation
          4. Click OK
    3. Configure Local Security Policy
      1. Select the Local Policies\Security Options\Network Access: Sharing and security model for local accounts policy
      2. Set the policy to Classic - local user authenticate as themselves
      3. Click OK
    4. Repeat these steps for the OPC Client computer
  9. Configuring OPCEnum
    1. Start Component Services on the Vista OPC Server computer
      1. In the tree structure Component Services\Computers\My Computer\DCOM Config right click on OPCEnum and click properties
        1. On the general tab change Authentication Level to Default
        2. Ensure Run Application on this computer is checked on location tab
        3. Click the Identity tab
          1. Select This User
          2. Browse to the local account OPC_Communication
          3. Provide the password in the Password and Confirm password field
          4. Click OK
    2. Repeat these steps on the OPC Client computer
  10. Start the TAC Vista OPC Server
    1. In Services right click on TAC Vista OPC Server and click start

For more OPC Server issues please see Vista OPC Server Installation and Known Issues.

A good overview of  OPC integration and the necessary COM and DCOM settings is located here.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4293
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore