Enabling IT Advisor monitoring through Data Center Expert
ITA server (on-premises only)
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Monitoring IT Advisor through Data Center Expert requires that you enable server communication in Webmin and in Data Center ExpertsnmpExpert.
Webmin Configuration
IT Advisor 8.x
Open the Webmin web interface.
Type the address of your IT Advisor server in a Web browser.
On the IT Advisor server's download page, click Server Configuration.
Log on to Webmin using the user credentials created during the installation.
In the left menu, select DC Operation>Setup.
Configure the server protocol settings, for example enable SNMPv1 and type community. The SNMP server requires a specific SNMP community from the monitoring systems. If the SNMP community is not correct, it will not reveal any information to the monitoring system. You can think of SNMP community as a password.
Tip
For added security, change the SNMP community to something other than "public" and make the monitoring system use this (see below).
Tip
For added security, disable SNMPv1 and configure SNMPv3.
Version 8.x
120133129_1148x250_360038620073.jpg
Data Center Expert configuration
In the Data Center ExpertDevice Discovery wizard, select the corresponding SNMPv1 or SNMPv3 settings, ensuring the community or username and password matches the one specified in the Webmin configuration (see above).
Set the Timeout to minimum 20 seconds to allow time for the server communication.