Capacity history KPI description

ITA Capacity

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA: Capacity
  • ITA Capacity
  • Capacity history KPI description
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Understanding estimated load and how it is calcula...
  • Redundancy examples
  • ITA: Capacity management
  • How power measurements are processed in IT Advisor
  • Finding the best location for a new server
  • Capacity reports
  • Capacity history KPIs over time
  • Capacity history KPI description
  • Advanced power configuration
  • Adjusted nameplate or predicted power
  • About predicted power
  • About power supply unit uncertainty
  • Understanding estimated load and how it is calcula...
  • Redundancy examples
  • ITA: Capacity management
  • How power measurements are processed in IT Advisor
  • Finding the best location for a new server
  • Capacity reports
  • Capacity history KPIs over time
  • Capacity history KPI description
  • Advanced power configuration
  • Adjusted nameplate or predicted power
  • About predicted power
  • About power supply unit uncertainty

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ITA Capacity
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1080 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Capacity history KPI description

Picard EcoStruxureIT
‎2019-10-02 07:05 AM

 

Capacity history data captured in EcoStruxure IT Advisor on a daily basis:

 

Capacity History Data Type (KPI) Area/license Description Data Equipment Level
Available U-space (AVAILABLE_USPACE) Capacity The currently available rack u-space Location, Room, Rack
Reserved U-space (RESERVED_USPACE) Capacity The rack u-space currently reserved by planned changes Location, Room, Rack
Total used U-space (USED_USPACE) Capacity The currently used rack u-space Location, Room, Rack
Available copper (AVAILABLE_COPPER_NETWORK) Capacity The number of available copper network ports in layer 2 & 3 network equipment Location, Room, Rack
Available fiber (AVAILABLE_FIBER_NETWORK) Capacity The number of available fiber network ports in layer 2 & 3 network equipment Location, Room, Rack
Available network ports (AVAILABLE_NETWORK_PORTS) Capacity The number of available network ports in layer 2 & 3 network equipment Location, Room, Rack
Used copper (USED_COPPER_NETWORK) Capacity The number of used copper network ports in layer 2 & 3 network equipment Location, Room, Rack
Used fiber (USED_FIBER_NETWORK) Capacity The number of used fiber network ports in layer 2 & 3 network equipment Location, Room, Rack
Used network ports (USED_NETWORK_PORTS) Capacity The number of used network ports in layer 2 & 3 network equipment Location, Room, Rack

Ambient temperature ((AMBIENT_TEMPERATURE)

Capacity

The calculated ambient ("background") temperature. This is the temperature in the room when not in the immediate vicinity of racks, coolers etc.

Room
Cold aisle capture index (COLD_AISLE_CAPTURE_INDEX) Capacity The cold aisle capture index UPS, Rectifier, Rack
Cooler capacity (COOLING_CAPACITY) Capacity The total capacity of coolers Location, Room
Cooler load (COOLING_LOAD) Capacity The calculated load of coolers Location, Room, CRAC
Hot aisle capture index (HOT_AISLE_CAPTURE_INDEX) Capacity The hot aisle capture index UPS, Rectifier, Rack
Inlet temperature (INLET_TEMPERATURE) Capacity The calculated inlet temperature UPS, Rectifier, Rack
Auxiliary load connected (AUXILIARY_LOAD_CONNECTED) Capacity Get the estimated load for auxiliary equipment. This is equipment that is not in racks, such as coolers Room
Estimated Load (ESTIMATED_LOAD) Capacity

Get the estimated load

Location, Room, Cage, UPS, Rectifier, PDU, Rack, Rack PDU, Internal Breakers
Estimated failover load (ESTIMATED_TRANSFERRED_LOAD) Capacity Estimated failover load Location, Room, UPS, Rectifier, PDU, Rack PDU
Estimated PSU uncertainty (RESERVED_FOR_PSU_UNCERTAINTY) Capacity Estimated power reserved for PSU uncertainty Location, Room, UPS, Rectifier, PDU, Rack, Rack PDU
Estimated distribution redundancy (RESERVED_FOR_DISTRIBUTION_REDUNDANCY) Capacity Estimated power reserved for distribution redundancy Location, Room, UPS, Rectifier, PDU, Rack, Rack PDU
Measured peak load (MEASURED_PEAK_LOAD) Capacity Get the measured peak power Location, Room, UPS, Rectifier, Rack, Cage, PDU, Rack PDU, Internal Breakers, Power Outlets
Measured failover load (MEASURED_TRANSFERRED_LOAD) Capacity Measured failover load Location, UPS, Rectifier, PDU
Measured peak load per phase(MEASURED_PEAK_LOAD_PER_PHASE) Capacity  Measured peak load per phase for three phase equipment. UPS, Rectifier, PDU, Rack PDU
Power capacity (POWER_CAPACITY) Capacity Power capacity Location, Room, UPS, Rectifier, PDU
Total estimated load (TOTAL_ESTIMATED_LOAD) Capacity Get the estimated load for equipment in racks and cages Location, Room, Rack, Cage
Total load connected (TOTAL_LOAD_CONNECTED) Capacity Get the total nameplate load of all equipment Location, Room, Rack
Estimated load per top redundancy item (ESTIMATED_LOAD_PER_TOP_LEVEL_ITEM) Capacity Estimated load for each top level redundancy item of a rack Rack
Estimated failover load per top redundancy item (FAILOVER_LOAD_PER_TOP_LEVEL_ITEM) Capacity Estimated failoverload for each top level redundancy item of a rack Rack 
Estimated PSU uncertainty per top redundancy item (RESERVED_FOR_PSU_UNCERTAINTY_PER_TOP_LEVEL_ITEM) Capacity Estimated power reserved for PSU uncertainty for each top level redundancy item of a rack Rack 
Measured average load per top redundancy item (MEASURED_FOR_TOP_LEVEL_ITEM_AVERAGE) Capacity Measured average load for each top level redundancy item of a rack Rack
Measured peak load per top redundancy item (MEASURED_FOR_TOP_LEVEL_ITEM_PEAK) Capacity  Measured peak load for each top level redundancy item of a rack Rack

Free outlets (FREE_POWER_OUTLET_CAPACITY)

 Capacity Number of free rack PDU power outlets grouped by outlet type Location, Room, Rack, Rack PDU, Internal Breakers

Used outlets (USED_POWER_OUTLET_CAPACITY)

 Capacity Number of used rack PDU power outlets grouped by outlet type Location, Room, Rack, Rack PDU, Internal Breakers

Total number of outlets

(TOTAL_POWER_OUTLET_CAPACITY)

 Capacity Total rack PDU power outlets capacity grouped by outlet type Location, Room, Rack, Rack PDU, Internal Breakers
Cancelled work orders (CANCELLED_WORK_ORDERS) Change Total number of cancelled work orders Location, Room
Work orders not started  (NOT_STARTED_WORK_ORDERS) Change Not started work orders, which are not overdue Location, Room
Work orders in progress (IN_PROGRESS_WORK_ORDERS) Change In progress work orders Location, Room
Overdue work orders (OVERDUE_WORK_ORDERS) Change Overdue work orders Location, Room
Completed work orders (COMPLETED_WORK_ORDERS) Change Total number of completed work orders Location, Room
Total work orders (TOTAL_WORK_ORDERS) Change Total number of work orders Location, Room
Revenue space (ROOM_CAGES_AREA) Co-Lo Room cages area. Location, Room
Sold space (ROOM_CLOSED_AREA) Co-Lo Room area sold to customers Location, Room
Power contracted with customers (ROOM_CLOSED_POWER_SOLD) Co-Lo Power already sold to customers for all equipment in a room. Location, Room
Closed racks (ROOM_CLOSED_RACKS) Co-Lo Racks in room sold to customers. Location, Room
Floor-mounted area (ROOM_FLOOR_MOUNTED_AREA) Co-Lo Room floor standing equipment total area Location, Room
Internal space (ROOM_INTERNAL_AREA) Co-Lo Room internal area. Location, Room
Internal racks (ROOM_INTERNAL_RACKS) Co-Lo Racks in room for internal usage. Location, Room
Open space (ROOM_OPEN_AREA) Co-Lo Room area open for new customers. Location, Room
Open racks (ROOM_OPEN_RACKS) Co-Lo Racks in room open for new customers Location, Room
Racks utilization (ROOM_RACKS_UTILIZATION) Co-Lo

Room racks utilization percentage. Racks utilization is sum of open, closed and reserved racks divided by total number of racks.

Location, Room
Reserved space (ROOM_RESERVED_AREA) Co-Lo Room area reserved for potential customers. Location, Room
Power reserved for customers (ROOM_RESERVED_POWER_SOLD) Co-Lo Power reserved for potential customers for all equipment in a room Location, Room
Reserved racks (ROOM_RESERVED_RACKS) Co-Lo Room area reserved for potential customers. Location, Room
Sellable area (ROOM_SELLABLE_AREA) Co-Lo Sellable area: sum of Open, Closed and Reserved area. Location, Room
Space utilization (ROOM_SPACE_UTILIZATION) Co-Lo Sellable area as a percentage of total room area. Location, Room
Closed racks (standalone) (ROOM_STANDALONE_CLOSED_RACKS) Co-Lo Racks in room sold to customers. Only standalone (outside cages) racks are counted. Location, Room
Internal racks (standalone) (ROOM_STANDALONE_INTERNAL_RACKS) Co-Lo Racks in room for internal usage. Only standalone (outside cages) racks are counted. Location, Room
Open racks (standalone) (ROOM_STANDALONE_OPEN_RACKS) Co-Lo Racks in room open for new customers. Only standalone (outside cages) racks are counted. Location, Room
Total racks (standalone) (ROOM_STANDALONE_RACKS) Co-Lo Room total racks number. Location, Room
Racks utilization (standalone) (ROOM_STANDALONE_RACKS_UTILIZATION) Co-Lo

Room racks utilization percentage. Racks utilization is sum of open, closed and reserved racks divided by total number of racks. Only standalone (outside cages) racks are counted.

Location, Room
Reserved racks (standalone) (ROOM_STANDALONE_RESERVED_RACKS) Co-Lo Room area reserved for potential customers. Only standalone (outside cages) racks are counted. Location, Room
Room area (ROOM_TOTAL_AREA) Co-Lo Room total area. Location, Room
Total contracted power (ROOM_TOTAL_POWER_SOLD) Co-Lo Total power sold to customers for all equipment in a room. Location, Room
Total racks (ROOM_TOTAL_RACKS) Co-Lo Total number of racks in a room Location, Room

Above temperature threshold (ABOVE_TEMPERATURE_THRESHOLD)

Cooling Optimize Relative time that the temperature for a rack exceeds its threshold (with a higher value) Rack
Below temperature threshold (BELOW_TEMPERATURE_THRESHOLD) Cooling Optimize Relative time that the temperature for a rack exceeds its threshold (with a lower value). Rack
PUE Energy Efficiency The PUE This is for energy systems only Location
Total network ports (TOTAL_NETWORK_PORTS) Operations The total number of network ports in layer 2 & 3 network equipment Room, Rack
Total U-space (TOTAL_USPACE) Operations The total rack u-space Location, Room, Rack
Total weight (TOTAL_WEIGHT) Operations The total weight of equipment Rack
Server quantity (SERVER_QUANTITY) Operations The number of servers mounted in racks Location, Room, Rack
Total IT Assets (TOTAL_ITOASSETS) IT Optimize Total number of servers and blades in a room Location, Room
Not associated IT Assets (UNPLACED_ITOASSETS) IT Optimize Number of not associated ITO assets Location, Room
IT Asset CPU utilization (UTILIZATION_CPU_AVG) IT Optimize Get the average CPU utilization (average of associated) Location, Room
IT Asset Power utilization (UTILIZATION_POWER_AVG) IT Optimize Get the power utilization (sum of associated averages) Location, Room
Consolidation Candidates (NUM_CONSOLIDATION_CANDIDATES) IT Optimize Number of retirement candidates (server utilization between 2% and 10%) Location, Room
Retirement Candidates (NUM_RETIREMENT_CANDIDATES) IT Optimize Number of retirement candidates (server utilization below 2%) Location, Room
Consolidation Candidates costs (POWER_COSTS_CONSOLIDATION_CANDIDATE_PRICE) IT Optimize The power costs for consolidation candidates Location, Room
IT Asset costs (tag) (ENERGY_COST_PER_TAG) IT Optimize Power costs for all servers with a given tag, per room Location, Room
IT Asset costs (POWER_COSTS_PRICE) IT Optimize The power cost setup for a room Location, Room
Retirement Candidates costs (POWER_COSTS_RETIREMENT_CANDIDATE_PRICE) IT Optimize The Power Costs for retirement candidates Location, Room

 

 

Capacity history data discontinued in version 8.0:

Capacity History Data Type (KPI) Area/license Description Data Equipment Level
Measured A-Feed average (MEASURED_A_FEED_AVERAGE) Capacity Get the measured average power on the A-feed UPS, Rack
Measured A-Feed peak (MEASURED_A_FEED_PEAK) Capacity Get the measured peak power on the A-feed UPS, Rack
Measured B-Feed average (MEASURED_B_FEED_AVERAGE) Capacity Get the measured average power on the B-feed UPS, Rack
Measured B-Feed peak (MEASURED_B_FEED_PEAK) Capacity Get the measured peak power on the B-feed UPS, Rack
Total reserved capacity (TOTAL_RESERVED_CAPACITY) Capacity Get the reserved capacity cf. capacity groups plus auxiliary equipment such as coolers Location, Room
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore