Redundancy examples

ITA Capacity

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA: Capacity
  • ITA Capacity
  • Redundancy examples
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ITA Capacity
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
776 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Redundancy examples

Picard EcoStruxureIT
‎2019-10-02 02:31 AM

Depending on the the nature of the modeled equipment, redundancy settings, and power path setup in IT Advisor, the capacity calculations can get quite complex. If you have a similar setup as one of these simplified examples, they may help you understand where the numbers in the tooltips come from.

 

Example 1: Multiple power supplies

The data center solution includes:

  • 1 large server, 3000 W load
  • 6 power supplies

Capacity values:

In previous versions of ITA, the Estimated Load would be very high. In the current version, it now works as follows:

  • Estimated Load: 500W on each connection (even load)
  • Estimated Load: 1000W on each connection (uneven load)
  • Power Supply Unit Uncertainty: 500W  (uneven load)

    If the server only uses half of the PSUs, the system must reserve up to: (3000W) / (6/2) = 1000W on each connection.
    This implies a Power Supply Uncertainty of 500W (because 1000W - Estimated Load = 500W).

To minimize the impact of PSU Uncertainty on the PDU, the PSU Uncertainty be only be carried upstream to the PDU in case of phase shifts.

Blade solutions:

If a blade enclosure includes bays powered by specific PSUs, the enclosure may only be using e.g. 2 out of 6 PSUs because the other bays are empty. In this case, the PSU Uncertainty reservation done by the system might be too small!

 

Example 2: Classic 2N and multiple power supplies

The data center solution includes:

  • 1 large server, 3000 W load
  • 6 power supplies
  • 3 connections to each of two separate rack PDUs

Capacity values:

  • Estimated load: 500 W on each connection
  • Failover load: 500 W on each connection
If the failover load can carry the full power supply uncertainty (as in this example), power supply uncertainty is not added to the calculations.
 

Example 3: Reservation for Distribution Redundancy

The data center solution includes:

  • 1 server, 1000 W load
  • 2 connections to two different PDUs (L1 and L2)
  • Both PDUs are connected to the same parent PDU

Capacity values:

Load overview
Load type and phase PDU 1 PDU 2 Parent PDU
Estimated Load, L1 500 W 0 W 500 W
Estimated Load, L2 0 W 500 W 500 W
Failover Load, L1 500 W 0 W -
Failover Load, L2 0 W 500 W -
Reserved for Distribution Redundancy, L1 - - 500 W
Reserved for Distribution Redundancy, L2 - - 500 W

 

On the parent PDU there is no failover load because additional load will not move to this PDU in case of a downstream failure. However, a phase shift might happen in case of a downstream failure because of the mixed phases on the server. (If the server would have been connected to only one single phase, there would be no need for reserving extra capacity.)

Example 4: Reservation for Distribution Redundancy with opposite effects

The data center solution includes:

  • 1 server, 1000 W load
  • 2 connections to two different PDUs (L1 and L2)

 

  • 1 server, 600 W load 
  • 2 connections to two different PDUs (L2 and L1)

 

Capacity values:

Load overview
Load type and phase PDU 1 PDU 2 Parent PDU
Estimated Load, L1 500 W 300 W 800 W
Estimated Load, L2 300 W 500 W 800 W
Failover Load, L1 500 W 300 W -
Failover Load, L2 300 W 500 W -
Reserved for Distribution Redundancy, L1 - - 200 W
Reserved for Distribution Redundancy, L2 - - 200 W

 

The two servers partly cancel out the need to reserve extra capacity.

 

 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of