Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
About predicted power
ITA Capacity
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Past trends in your equipment's measured peak power data from DCE or other external system integration are used to predict the future power demand.
By default, the system bases the calculations on historic data from the last 90 days and predicts 30 days in to the future. You can adjust these settings in Preferences > External Systems > Measurement Trending.
Note: The graphs here serve as examples only. They do not reflect any graphs available in ITA or in reports.
The first graph illustrates the predicted power concept and the rest are examples of special scenarios to explain why your calculations behave the way they do.
105471637_693x250_360036174414.png
Predicted power (measured peak power consumption on rack PDU)
How is the prediction affected when adding the first server to an empty rack?
Due to the added load, the trend would become unrealistically steep over a period of 30 days. Therefore, a maximum factor of 1.5 (by default) is used to keep the trend within a more appropriate range.
Note: When adding the new server, you may see some unexpected values while you're editing. This happens because the system falls back on adjusted nameplate calculations until you save your changes or, if you have IT Advisor: Change, until you execute the pending change.
105471638_683x250_360036174414.png
Predicted power (when adding the first server to a rack)
How is the prediction affected when your measurements are stabile?
If the measurements have been stabile for the period of time the system has data for this rack, the system does not rely on this data to be realistic until there's measured data for at least 90 days (default).
The trend line would become almost flat. Therefore, a minimum factor of 1.2 (by default) is used as a safety margin to keep the trend line within a more appropriate range. A lower threshold of 1 also prevents the trend line from becoming negative.
However, if the measurements have been stabile for an even longer period of time (more than 90 days by default), the data is assumed to be highly reliable and the safety margin is disregarded.
105471639_670x250_360036174414.png
Predicted power (when measurements are stabile)
How is the prediction affected when removing a server from a rack?
Due to the reduction in load, the trend would drop unrealistically over a period of 30 days.
When you have removed a server from a rack and saved your changes, the trend line will no longer include values from the last 90 days but only values since the server was removed to exclude values from removed equipment no longer relevant to you.