Changing Alarm Limit Does Not Immediately Raise an Alarm
Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 08:40 PM
📖 Home Back
Alarms are only raised when the alarm limit is transgressed. So if the limit is changed, to then make the point above (or below as appropriate) the new limit, the alarm will not be raised until the point value has gone below that limit and then been raised above it again.
If you modify one of the alarm limits such that the point value is now in alarm, the alarm will not be generated. This functionality is by design.
Go: Home Back
Alarms are only raised when the alarm limit is transgressed. So if the limit is changed, to then make the point above (or below as appropriate) the new limit, the alarm will not be raised until the point value has gone below that limit and then been raised above it again.
If you modify one of the alarm limits such that the point value is now in alarm, the alarm will not be generated. This functionality is by design.