We have installed our first COMX200 and is publishing it to REM. We have upgraded it to the latest firmware.
For some unknown reason all values are divided by 1000! (See bold values in the output file!)
please can you have a look why this is happening??? This is extremely frustrating!
I have also attached the commissioning procedure we have followed. We use 30 min standard in SA.
OUTPUT CUT....
,20140703040000,"00030216333762_Resource-0\Aerostructures Cooling Towers|1601\Active Energy Into the Load",OK,E,kWh,0.001,00000030,2,201407030300,,3.1270000000004075,,,3.1279999999997017
,20140703040000,"00030216333762_Resource-0\Aerostructures Cooling Towers|1605\Reactive Energy Into the Load",OK,E,kVArh,0.001,00000030,2,201407030300,,8.423999999999978,,,8.434999999999945
...
Accepted Solutions

Posted: 2014-08-24 11:47 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi, Arjan
This issue is solved with the new firmware V1.1.20, can be found at the following link:https://schneider-electric.box.com/s/vp659224ty3ss6ql4fj4
Note that :This forum is not monitored by our EMS support team, so we recommend you to send your requests to: global-ems-solutions-support@schneider-electric.com
which guarantees the answer in time according to SE requirements.
Best Regards
Lazaro
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Unfortunately, we have the same problem!!! ..and also for us is the first COM'X200 installed.
We have already opened a support request to 'global-ems-solutions-support' (No answers yet).
Here are the details:
Case Reference #: 11596575
Subject: Re: Com'X200 - Energy Operation Online
Date Created: 26.6.2014
Case ID: ref:_00DA0abSm._500A0LN41k:ref
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I'm sitting with a confused client! It seems clear to me that the EBX200 was not tested in this area? @Schneider Team is there any news regarding a fix?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello, I'm the quality leader for COM'X offer, we are investigating this issue, we will go back to you soon.
Catherine
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
thank you very much Catherine,
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Arjan,
I've only been pushing to EO, so haven't seen this. But can easily test. Was it with any type of meter? Which one are you using?
A work around would be to push to "3rd party" which uses the EGX300 file format. Since REM supports the EGX file format, it should do the trick (even though I personally prefer the CMEP file format which is more compact).
3rd party is the "CSV export" option.
At least until we have more time to investigate, you can sort out your customer.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
We have fixed the problem. This will be corrected in V1.1.20 of COM'X 200 firmware which will be available at the end of the month on SEC.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Catherine,
What about the strange timestamping of the Com'X that we have found on a site (was also reported on the SEC but I never got back an answer for this issue), will this also be corrected with the new version? I also made some tests here in the office with the same result. It seems that data have been sent randomly in the device (for example you can have 4 devices connected to the Com'X. Two have on an hourly base 4 entries, beginning with XX:00 and the rest of the devices with XX:15 or one device has suddenly only 3 entries and then on the next run 5).
Thanks
Daniel
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Daniel,
I can see in SEC that Jef Maubert has started working on this issue, I will
check with him but he is vacation until the 21th of July.
you can also report your issue to the Customer Care Center at
global-ems-solutions-support@schneider-electric.com
Catherine
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
OK, thanks. I will see.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Laurent,
We are trying the CSV export option now, but I see the COMX'200 is exporting it as a .ZIP file, and it seems that EVO/REM doesn't support ZIP files.
What now.......?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Laurent,
this "trick" is not working, since the EBX200 is exporting CSV not exactly the same as the EGX300 used to do.
Looks like the "return" characters have been stripped from the CSV file, notice in the screenshot below when you open them up in notepad.
Also, the rem / evo server rejects them. I have set the correct date/time format to match egx300 format.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Arjan, as I'm sure you are aware I had to remove the 4 x COMX's from site as they are not suited to work on the REM platform. The client was putting pressure on us to complete the installation so we replaced them with the older non Schneider modems that work!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Guys,
I was promised firmware end of july. Any news?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi james, i have received it now from global.
Thanks
Sent from my iPad
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi ArjanI
I sent the nwe firmware 1.1.20 to two customer and the problem of the measuring devided for 1000 was solved. Now in REM we read the measuring rightly,
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Com'X 200 Version 1.1.20 is now available on the Shopping Kiosk, or here on the SEC: https://powersolutionscommunity.schneider-electric.com/docs/DOC-2746
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi James, does this release also fix the CSV file format (EGX file format) issue that was discovered in this thread?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Arjan. I apologize that you are experiencing these issues. I will escalate to the engineering/quality team today.
Have you created any support ticket for this issue with global technical support?
James

Posted: 2014-08-24 11:47 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi, Arjan
This issue is solved with the new firmware V1.1.20, can be found at the following link:https://schneider-electric.box.com/s/vp659224ty3ss6ql4fj4
Note that :This forum is not monitored by our EMS support team, so we recommend you to send your requests to: global-ems-solutions-support@schneider-electric.com
which guarantees the answer in time according to SE requirements.
Best Regards
Lazaro
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi lazaro,
We are using firmware 1.1.20
The issue still persists.
Sent from my iPad
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
HI James,
yes:
Schneider Electric Case # 12955857: COMX200 Negative data issue on pulse
inputs
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I'm now going to remove my 4th ComX from site!! This has been very embarrassing and costly for my company (not to mention Schneider). I cant believe that the ComX hasn't been field tested before released.
As I have mentioned in other posts the ComX has great potential but its not there yet.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Nigel,
I fully agree with you as I have a little bit the same feelings about this product!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi guys...I completely understand your concerns. The Com'X 200 Engineering and Quality teams are aware of these issues and are working diligently to solve the problems you are facing.
James
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Nigel, if the issue that makes you remove the COM'X is the division by 1000 in REM , it is solved with V1.1.20
best regards
Catherine
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello all,
I feel that the thread has drifted from the initial topic which was the REM scaling problem. From my point of view this issue is solved with V1.1.20. Do you agree ?
I propose to close this topic and I will make a dashboard with the issues that I will find here or that you send me by mail.
I will share this dashboard in a BOX, and you will be able to complete/precise the issues. I will update the status of the issues in this dashboard.
What do you think ?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I think this is best. Thanks Catherine.