Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
Options
  • Mark all as New
  • Mark all as Read
  • Float this item to the top
  • Subscribe
  • Bookmark
  • Invite a Friend
  • Threaded format
  • Linear Format
  • Sort by Topic Start Date
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • Indonesia 204
  • Brazil 11
  • India 11
  • Singapore 4
  • Spain 3
  • Russia 1
  • Italy 1
  • United Kingdom 1
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All
Related Products
Thumbnail of BlokSet
Schneider Electric
BlokSet
4
Thumbnail of Prisma iPM
Schneider Electric
Prisma iPM
3
Thumbnail of SM6 Switchgear
Schneider Electric
SM6 Switchgear
3
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Expert on Demand for Standards & Regulations

Start a Topic
  • All
  • Solved
  • Unsolved
  • Unanswered
fabioribeiro
Ensign fabioribeiro Ensign

Olá! Bem vindo à nossa Comunidade Exchange Brasil!

Fique à vontade para postar as suas dúvidas conosco que teremos o prazer de ajudar! 🙂 Somos uma comunidade de especialistas técnicos focados em apoiar engenharias e projetistas no esclarecimento de no...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
2295 1 0

2021-04-26

Nikita_Sydney
Crewman Nikita_Sydney Crewman

Welcome to the India Page for Expert On Demand

Dear Premier Consultants, Have you always been interested to know about the standards that ensure electrical safety and power availability? Are you curious about the latest international recognized ...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
930 2 0

2021-07-06

sesa476158_brid
sesa476158_brid Cadet

Welcome to Expert on Demand!

Dear Premier Consultants from Singapore, We are happy to offer you the opportunity of raising specific questions about standardization. We have created this forum so that you can shar...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
804 0 0

2021-07-08

Widiyatmoko
Ensign Widiyatmoko

Selamat datang di Expert on Demand !

Selamat datang di Expert on Demand ! Schneider Electric Indonesia menyediakan Forum ini sebagai media untuk berbagi dan berdiskusi mengenai Standardisasi dan Regulasi. Bersama @HelvinHermanT dan Team k...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
1391 1 2
Latest Reply: Widiyatmoko

Anonymous user
Anonymous user

Bienvenidos al Foro de Exchange de Normativa

Hola, Soy Xavier Barnils, responsable de Prescripción de Schneider Electric Iberia. Hemos creado este foro, para que podáis compartir vuestras preguntas del ámbito de normativa. Junto a @Anonymous us...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
1178 0 0

2021-06-16

Jean_Commeignes
Administrator Jean_Commeignes Administrator

Welcome to Expert on Demand!

Dear Premier Consultants, We are happy to offer you the opportunity of raising specific questions about standardization. Please respect two conditions to have your question answered: Please selec...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
2349 2 0

2021-03-09

Solved
CitraR
Ensign CitraR

Torsi untuk koneksi listrik

Mohon dapat dijelaskan mengapa kita perlu melakukan pengecekan besaran torsi pada koneksi listrik. Mengapa tidak hanya cukup dikencangkan saja oleh teknisi pemasangan. Terima kasih
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
3263 0 3
Latest Reply: HelvinHermanT

HelvinHermanT
Admiral HelvinHermanT Admiral

Peningkatan Instalasi Tegangan Menengah (MV) akibat Perkembangan pada ...

Seperti yang kita ketahui bersama bahwa, Standar harus berkembang untuk memastikan instalasi MV yang lebih aman dan efisien. Hampir semua produk yang digunakan orang dalam kehidupan sehari-hari – s...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
672 0 1
Latest Reply: HelvinHermanT

AntoniusH
Ensign AntoniusH

Belanja Barang Schneider secara online

Salam Pak, Apakah ada rekomendasi untuk membeli barang Schneider di Toko Online seperti Tokopedia, Lazada, dll ? Terlalu banyak toko bingung saya, mana yang jual barang murah tetapi asli 😁 Terima kasi...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
859 0 1
Latest Reply: HelvinHermanT

RitaR
Ensign RitaR

Perbedaan Kabel isi 2 atau 3 ?

Selamat Siang, Saat saya mau membeli kabel extension untuk rumah, saya ditawarkan oleh toko mau yang dengan kabel isi 2 atau isi 3. Mohon dijelaskan perbedaan Kabel Extension dengan Kabel isi 2 dan Kab...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
20408 0 1
Latest Reply: HelvinHermanT

Solved
KKS
Ensign KKS

Apa perbedaan MCB Original, KW Super, KW 1

Selamat Siang, Mohon diberikan penjelasan perbedaan MCB Original, KW Super, KW 1 dan KW 2. Apa saja perbedaanya dan bagaimana cara membedakannya ? Trims.
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
6360 1 3
Latest Reply: HelvinHermanT

RitaR
Ensign RitaR

Mengapa ikan tidak kesetrum di akuarium ?

Selamat Siang, Tanya donk. Mengapa kita saat kita memegang air aquarium terasa kesetrum, sedangkan ikan di aquarium baik baik saja dan tidak mati kesetrum. Terima kasih.
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
10167 0 2
Latest Reply: HelvinHermanT

CitraR
Ensign CitraR

Strategi meminimalisir pemadaman pada instalasi listrik

Selamat Siang, Seiring dengan berjalannya waktu, pada suatu saat harus melakukan pemadaman yang diakibatkan kerusakan atau jadwal perawatan pada Circuit Breaker yang ada, Apakah bisa sharing cara untuk...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
1226 1 5
Latest Reply: HelvinHermanT

Yulianti
Crewman Yulianti

Menentukan rating Ampere breaker pada aplikasi pompa hidran kebakaran

Dear Pak @HelvinHermanT , Saya ingin menanyakan bagaimana menentukan rating Ampere breaker pada aplikasi pompa hidran kebakaran mengacu pada standard SNI 03-6570 tahun 2001 dan PUIL 2011? Ada klausal p...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
940 1 1
Latest Reply: HelvinHermanT

Yulianti
Crewman Yulianti

MCB untuk beban penerangan

Dear Pak @HelvinHermanT , Dalam pemilihan MCB untuk beban penerangan sebaiknya mengacu pada kurva C atau D ?
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
689 0 1
Latest Reply: HelvinHermanT

Solved
HelvinHermanT
Admiral HelvinHermanT Admiral

Withdrawable atau Fixed Circuit Breaker ?

Pertanyaan mengenai mana yang lebih baik ? Pemutus Arus tipe dapat ditarik / Withdrawable Circuit Breaker atau Pemutus Arus tipe Magun / Fixed Circuit Breaker ? Apa saja sih kelebihan dan kek...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
2358 0 6
Latest Reply: HelvinHermanT

Martinmx
Lieutenant JG Martinmx

Error Web report Building operation

Hello, Install the reporting server for building operation but when the installation is finished it triggers an error, in the panel I have the alarm "Web server failure" and when I want to generate a n...
Power Distribution IEC icon_circle Expert on Demand for Standards & Regulations
805 0 0

2022-06-07

  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 22
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore