Withdrawable atau Fixed Circuit Breaker ?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Withdrawable atau Fixed Circuit Breaker ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
105
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
VickyTanzil
Ensign VickyTanzil Ensign
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Solved
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-23 11:48 PM . Last Modified: ‎2022-05-24 03:20 AM

0 Likes
6
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-23 11:48 PM . Last Modified: ‎2022-05-24 03:20 AM

Withdrawable atau Fixed Circuit Breaker ?

Pertanyaan mengenai mana yang lebih baik ?

 

Pemutus Arus tipe dapat ditarik / Withdrawable Circuit Breaker

 

atau

 

Pemutus Arus tipe Magun / Fixed Circuit Breaker ?

 

 

Apa saja sih kelebihan dan kekurangannya ?

 

Kapan sebaiknya kita memilih menggunakan tipe Fixed atau Withdrawable ?

 

Mari kita bahas dan diskusikan mana yang lebih baik 🙂

 

 

 

 

@Dwinanto_Setyadi @JuneventV @faisalamir @HendySE @FerryKurniawan @Andry @Dhana-Putra @Widiyatmoko @Widiyatmoko1 @reinierliman @Yulianti @Deddy @Anonymous user @rinonainggolan @Anonymous user 

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-23 11:54 PM . Last Modified: ‎2022-05-24 12:19 AM

0 Likes
5
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-23 11:54 PM . Last Modified: ‎2022-05-24 12:19 AM

Kalau dari segi harga,

Pemutus Arus tipe dapat ditarik / Withdrawable Circuit Breaker, lebih mahal harganya.

 

Lebih mahal karena ada beberapa part tambahan dibandingkan Pemutus Arus tipe Magun / Fixed Circuit Breaker, seperti :

 

Tambahan kontak utama / Main contact : Contact Finger Female & Male

Tambahan Penutup Pengaman / Safety Shutter 

Tambahan silih kunci mekanis / Mechanical Interlock.

Tambahan lajur mekanis untuk memasukkan pemutus arus.

dan lain lain.

 

Pastinnya biaya produksi lebih mahal Withdrawable dibandingkan Fixed Circuit Breaker.

 

Main contact.jpg

racking mechanism.pngInterlock.jpgshutter.jpg

 

See Answer In Context

  • Tags:
  • bahasa Indonesia
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KKS
Ensign KKS
Ensign

Posted: ‎2022-06-07 01:13 AM . Last Modified: ‎2022-06-07 01:21 AM

In response to HelvinHermanT
1 Like
2
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-07 01:13 AM . Last Modified: ‎2022-06-07 01:21 AM

Ada juga yang memilih Tipe Fixed karena penggunaan breaker tersebut pada area yang lingkungan korosif.

 

Jika menggunakan tipe withdrawable pada area korosif, maka cenderung timbul masalah pada area kontak antara kontak pada Breaker dengan kontak pada chassis dikarenakan lingkungan yang korosif.

 

 

images.jpg  images (1).jpg

 

 

Mereka lebih memilikh menggunakan tipe Fixed untuk meminimalisir korosif pada area kontak karena tipe fixed sambungannya menggunakan Busbar yang disambung fixed / rapat dengan baut (bolt).

 

images (3).jpg

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-23 11:54 PM . Last Modified: ‎2022-05-24 12:19 AM

0 Likes
5
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-23 11:54 PM . Last Modified: ‎2022-05-24 12:19 AM

Kalau dari segi harga,

Pemutus Arus tipe dapat ditarik / Withdrawable Circuit Breaker, lebih mahal harganya.

 

Lebih mahal karena ada beberapa part tambahan dibandingkan Pemutus Arus tipe Magun / Fixed Circuit Breaker, seperti :

 

Tambahan kontak utama / Main contact : Contact Finger Female & Male

Tambahan Penutup Pengaman / Safety Shutter 

Tambahan silih kunci mekanis / Mechanical Interlock.

Tambahan lajur mekanis untuk memasukkan pemutus arus.

dan lain lain.

 

Pastinnya biaya produksi lebih mahal Withdrawable dibandingkan Fixed Circuit Breaker.

 

Main contact.jpg

racking mechanism.pngInterlock.jpgshutter.jpg

 

  • Tags:
  • bahasa Indonesia
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AntoniusH
Ensign AntoniusH
Ensign

Posted: ‎2022-05-26 11:43 PM . Last Modified: ‎2022-05-26 11:45 PM

In response to HelvinHermanT
1 Like
4
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-26 11:43 PM . Last Modified: ‎2022-05-26 11:45 PM

Kalau saya memilih Withdrawable karena akan mudah saat perawatan, tinggal di tarik CBnya, jadi tidak perlu pemadaman pada panel utama.

 

Lain halnya jika kita melakukan perawatan pada CB Fix type, memerlukan pemadaman pada sumber listrik dari panel utama. Hal ini karena untuk keamanan dalam perawatan karena busbarnya ada power.

 

Seperti postingan diatas, pada tipe Withdrawable ada safety shutter (Warna merah) yang melindungi kita untuk dapat mengakses ke bagian yang ada power.

 

Bisa dilihat proses memasukkan dan mengeluarkan CB pada video youtube ini.


  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-30 01:04 AM

In response to AntoniusH
0 Likes
3
1473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-30 01:04 AM

Terima kasih Pak @AntoniusH, memang dengan tipe Withdrawable bisa mudah saat perawatan.

 

Bahkan bukan hanya saat perawatan, saat terjadi perbaikan juga bisa lebih mudah dengan menggunakan tipe withdrawable. Tinggal CB di tarik keluar dan dilakukan perbaikan pada CB tersebut tanpa harus memadamkan busbar utama yg akan mengakibatkan pemadaman total.

 

Dengan CB berada diluar, perbaikan dan perawatan dapat dengan mudah dilakukan.

 

 

Annotation 2022-05-30 150256.jpg

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KKS
Ensign KKS
Ensign

Posted: ‎2022-06-07 01:13 AM . Last Modified: ‎2022-06-07 01:21 AM

In response to HelvinHermanT
1 Like
2
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-07 01:13 AM . Last Modified: ‎2022-06-07 01:21 AM

Ada juga yang memilih Tipe Fixed karena penggunaan breaker tersebut pada area yang lingkungan korosif.

 

Jika menggunakan tipe withdrawable pada area korosif, maka cenderung timbul masalah pada area kontak antara kontak pada Breaker dengan kontak pada chassis dikarenakan lingkungan yang korosif.

 

 

images.jpg  images (1).jpg

 

 

Mereka lebih memilikh menggunakan tipe Fixed untuk meminimalisir korosif pada area kontak karena tipe fixed sambungannya menggunakan Busbar yang disambung fixed / rapat dengan baut (bolt).

 

images (3).jpg

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-06-08 08:26 PM

In response to KKS
0 Likes
1
1451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 08:26 PM

Terima kasih Pak @KKS ,

 

Memang saya juga pernah ketemu customer yang menggunakan argumen yang sama untuk memilih Fixed CB. Masuk akal sih alasannya.

 

Mungkin lebih baik untuk bertanya lebih dahulu mengenai spesifikasi ketahanan produk yang akan  digunakan terhadap kondisi lingkungan dimana produk akan dipasang.

 

Juga bisa ditambahkan perindungan oleh Panel Listrik dengan tingkat IP yang sesuai. (Contoh IP54).

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-06-08 08:29 PM

In response to HelvinHermanT
0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 08:29 PM

Sebagai contoh untuk Produk ACB Mastrpact MTZ bisa dilihat spesifikasinya :

Masterpact MTZ—Extreme Atmospheric Condition

MTZ Extreem Atmosphere condition.jpg

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of