Strategi meminimalisir pemadaman pada instalasi listrik

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Strategi meminimalisir pemadaman pada instalasi listrik
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Expert on Demand for Standards & Regulations
Start a Topic
CitraR
Ensign CitraR
Ensign

Posted: ‎2022-05-30 01:13 AM

1 Like
5
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-30 01:13 AM

Strategi meminimalisir pemadaman pada instalasi listrik

Selamat Siang,

 

Seiring dengan berjalannya waktu, pada suatu saat harus melakukan pemadaman yang diakibatkan kerusakan atau jadwal perawatan pada Circuit Breaker yang ada,

 

Apakah bisa sharing cara untuk meminimalisir pemadaman pada beban ?

 

 

Terima kasih

Salam,

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-30 01:20 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-30 01:20 AM

@Dwinanto_Setyadi @faisalamir @HendySE 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KKS
Ensign KKS
Ensign

Posted: ‎2022-06-07 12:24 AM . Last Modified: ‎2022-06-07 12:33 AM

2 Likes
3
1088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-07 12:24 AM . Last Modified: ‎2022-06-07 12:33 AM

Jika ada dana banyak sih sistem bisa dibuat double outgoing. Tetapi untuk membuat sistem seperti ini perlu biaya yang lebih besar karena perlu dua outging CB pada setiap beban.

 

Jadi jika satu outgoing breaker rusak, beban tetap bisa menyala dengan di suplai dari breaker yang satu lagi.

 

Saya pernah lihat sistem ini di perusahaan oil and gas yang memang punya dana lebih besar dan tidak ingin pompanya mati. 

Doube outgoing.jpg

  • Tags:
  • bahasa Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-06-08 08:33 PM

In response to KKS
0 Likes
2
1080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 08:33 PM

Terima kasih sharingnya Pak KKS,

 

Memang dengan double outgoing kita bisa memindahkan suplai listrik dari CB A1 ke CB A2 atau sebaliknya saat salah satu dalam perbaikan atau perawatan.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-06-08 08:51 PM

In response to HelvinHermanT
0 Likes
1
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 08:51 PM

Saya pernah menawarkan suatu strategi untuk meminimalisir pemadaman pada instalasi listrik dengan Manajemen Stok (Cadangan).

 

Jika suatu instalasi memiliki 10 buat ACB Tipe Drawout (Tipe dapat ditarik) yang mana terdiri dari 4 unit 1250A, 4 unit 3200A dan 2 unit 5000A. Maka kita bisa membuat strategi menyediakan stok ACB sebagai cadangan jika terjadi masalah dalam salah satu ACB yang terpasang.

 

Besarnya jumlah stok tergantung dari tingkat kritikal dari beban yang di suplai atau dampak yang ditimbulkan jika terjadi pemadaman. Tentu saja tingkat kritikal beban lampu penerangan gudang lebih kecil daripada tingkat kritikal pada beban lampu penerangan sebuah Shopping Mall.

 

Dari tingkat kritikal tersebut bisa kita tentukan jumlah stok ACB berdasarkan populasi rating ampere yang ada.

 

Jika terjadi kerusakan kita bisa menggantikan ACB tersebut dengan ACB dari stok atau cadangan sementara ACB yang rusak dalam proses perbaikan.

 

Saya melihat metode ini juga akan digunakan dalam strategi Swab Baterai pada Sepeda Motor listrik dimana pelanggan cukup membayar kontrak kepada penyedia jasa untuk menukarkan baterai yang kosong dengan yang sudah penuh yang tersedia di area area tertentu.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-06-16 11:56 PM

In response to HelvinHermanT
0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-16 11:56 PM

Strategi "Scheduled Downtime (Pemadaman Terjadwal) vs Unplanned Downtime (Pemadaman Tidak Terjadwal)"

 

Dalam Strategi Maintenance / Perawatan Peralatan Listrik, lebih baik kita merencanakan penjadwalan pemadaman (Scheduled  Downtime) untuk melakukan perawatan dibandingkan dengan Pemadaman tidak Terduga (Unplanned Downtime) atau pemadaman akibat kerusakan pada sistem kelistrikan.

 

Dalam Pemadaman yang terjadwal (Scheduled Downtime) kita bisa mempersiapkan segala sesuatunya sehingga tindakan perawatan bisa dilakukan secara menyeluruh dan dalam waktu yang effisien.

 

Dibandingkan dengan Pemadaman tidak terduga akibat kerusakan pada sistem yang pastinya pemulihan akan lebih lama dikarenakan banyak faktor seperti : Ketidaksiapan Personil (Saat liburan), ketidak siapan suku Cadang, Ketidak siapan Produk Pengganti, dll.

 

Biaya yang dikeluarkan akibat Pemadaman tidak terduga pastinya lebih besar karena memerlukan penggantian part / barang yang rusak. Belum lagi Kerugian produksi (kerusakan bahan baku akibat terhentinya produksi),  Kerugian bisnis akibat keterlambatan pengiriman, Dampak yang mungkin timbul akibat kerusakan seperti kebakaran / ledakan.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore