EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2024-04-05 04:43 AM
I've configured de PUE calculation in DCO 8.1 with sensor and values are showed in all total rows but the graph in web client shows zero.
(CID:125213596)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2024-04-05 04:43 AM
Hi Enric,
Many thanks for the screen capture. It seems your PUE is showing the correct value (which is practically close to zero). The Total Power in (according to your screen capture) is 69.7 and the total IT Load is 10290. That would give us the PUE = 69.7 / 10290 = 0.00677.
Basically the issue is with your power units. Your Power in units are in kW, but the IT Loads are in W.
Change the Multiplier (to either 0.001 for IT Loads or 1000 for Power in) so both Power In and IT Load to have the same power units.
Kind regards
(CID:126159001)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2024-04-05 04:43 AM
Hi Enric,
Can you please add some screen captures so we can follow your steps and see the issue you are seeing. (please mask the sensitive data such as IP address), thanks
Kind regards
(CID:125213946)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2024-04-05 04:43 AM
Tomorrow I'll a connection with the customer and I'll take screen captures.
Thanks,
Enric Climent
(CID:126158633)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2024-04-05 04:43 AM
Good morning Jef,
Here you can see the PUE configuration screen capture.
Regards,
Enric Climent
(CID:126158963)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2024-04-05 04:43 AM
Hi Enric,
Many thanks for the screen capture. It seems your PUE is showing the correct value (which is practically close to zero). The Total Power in (according to your screen capture) is 69.7 and the total IT Load is 10290. That would give us the PUE = 69.7 / 10290 = 0.00677.
Basically the issue is with your power units. Your Power in units are in kW, but the IT Loads are in W.
Change the Multiplier (to either 0.001 for IT Loads or 1000 for Power in) so both Power In and IT Load to have the same power units.
Kind regards
(CID:126159001)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 12:02 AM . Last Modified: β2023-10-22 04:24 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.