our customer has multiple leak ropes connected with one Netbotz 570. what will happen if one cable cut/damage, for example total 5 cables if number 3 become faulty (cut/damage) what will happen with other cables and what will be the alarm on DCE.
(CID:143756624)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:11 PM . Last Modified: β2024-04-03 02:44 AM
Hello Ali,
The leak rope sensors work on a conductivity basis. If a leak rope is broken at any point, the leak rope should still monitor for leaks, but only up to the broken point.
Kind Regards,
Cory
(CID:143756634)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:11 PM . Last Modified: β2024-04-03 02:44 AM
Just to add to Coryβs answer, if there was somehow a short because of the damage, the sensor would report a leak until the damaged part is removed.
(CID:143756698)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:11 PM . Last Modified: β2023-10-22 04:18 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.