Siren/Hooter integration with RackMonitor

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Siren/Hooter integration with RackMonitor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

0 Likes
7
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

Siren/Hooter integration with RackMonitor

hey everyone 

just need a quick help......My client wants me to add a Siren or Hooter with RM 250 or 450 to activate when leak rope alarm occurs. I saw Alarm Beacon option in installation manual, but they need it to generate sound on any event.

anybody plz give me an idea how do I integrate a 220V AC or 12 to 24 V DC siren or hooter with Rack Monitor.

Thanks in advance,

M. Raza Khan

(CID:120131788)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

0 Likes
5
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

Dear Raza,

I have shared a document on how to connect Buzzer/Sound Alarm to Netbotz 200/450/570. 

I hope it helps. Please let me know if you are facing any issue in accessing the page. 

Regards,

Bala

(CID:120131896)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

Dear Bala,

I'll try this & will let you know by monday if it works.

Thanks a lot.

Regards,

Raza Khan

(CID:120132734)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

Hello Bala,

I tried it but unfortunately it didn't work.
I've attached an image to show where I've terminated the Siren & jumper.

Also, the siren requires 12V DC. & everything else was done exactly what you explained in your procedure.

Please guide me if Im missing something.

Kindly treat this as urgent matter.

Thanks alot for the support.

Regards,
Raza Khan

 

(CID:120133590)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

Hi Raza-Is your siren working when you directly power by 12 Vdc from Netbotz appliance? Have you tried NC relay output? 

I could make it work, and our team also make it work with the same instructions. Netbotz supply from the 12V and 24V connections are capable of only 75mA total output.  

I also let other community experts to suggest. 

(CID:120133631)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

hey there,

well I tried but couldn't make it work with direct power, may be im mistaking plz guide me.
(by the way its working with external power)

No I didn't try NC output, is it possible if I give you TeamViewer session so you'll verify the relay output settings in Advanced View & its association with Leak Rope sensor ?

Please this has become a serious issue & my client is not happy with it. I really want to close this matter now !

Regards,

Raza Khan

(CID:120134104)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2024-04-08 12:23 AM

I would suggest you to contact your country technical support if you require further support in configuring the siren through dry contacts of Netbotz appliance. I also let other community experts to suggest for your query. 

(CID:120134177)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2023-10-22 03:56 AM

0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 PM . Last Modified: ‎2023-10-22 03:56 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of