EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
hey everyone
just need a quick help......My client wants me to add a Siren or Hooter with RM 250 or 450 to activate when leak rope alarm occurs. I saw Alarm Beacon option in installation manual, but they need it to generate sound on any event.
anybody plz give me an idea how do I integrate a 220V AC or 12 to 24 V DC siren or hooter with Rack Monitor.
Thanks in advance,
M. Raza Khan
(CID:120131788)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
Dear Raza,
I have shared a document on how to connect Buzzer/Sound Alarm to Netbotz 200/450/570.
I hope it helps. Please let me know if you are facing any issue in accessing the page.
Regards,
Bala
(CID:120131896)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
Dear Bala,
I'll try this & will let you know by monday if it works.
Thanks a lot.
Regards,
Raza Khan
(CID:120132734)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
Hello Bala,
I tried it but unfortunately it didn't work.
I've attached an image to show where I've terminated the Siren & jumper.
Also, the siren requires 12V DC. & everything else was done exactly what you explained in your procedure.
Please guide me if Im missing something.
Kindly treat this as urgent matter.
Thanks alot for the support.
Regards,
Raza Khan
(CID:120133590)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
Hi Raza-Is your siren working when you directly power by 12 Vdc from Netbotz appliance? Have you tried NC relay output?
I could make it work, and our team also make it work with the same instructions. Netbotz supply from the 12V and 24V connections are capable of only 75mA total output.
I also let other community experts to suggest.
(CID:120133631)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
hey there,
well I tried but couldn't make it work with direct power, may be im mistaking plz guide me.
(by the way its working with external power)
No I didn't try NC output, is it possible if I give you TeamViewer session so you'll verify the relay output settings in Advanced View & its association with Leak Rope sensor ?
Please this has become a serious issue & my client is not happy with it. I really want to close this matter now !
Regards,
Raza Khan
(CID:120134104)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2024-04-08 12:23 AM
I would suggest you to contact your country technical support if you require further support in configuring the siren through dry contacts of Netbotz appliance. I also let other community experts to suggest for your query.
(CID:120134177)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:54 PM . Last Modified: β2023-10-22 03:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.