We have a Netbotz 570. We can access the web interface and connect to the device with advanced view. It detects when we plug in a camera to one of the USB ports. It does not detect and devices that we plugged into the universal sensor ports or the A-Link port. It does supply power from the ports since it does power up our temp/humidity sensor. It is running the latest firmware. Has anyone run into this problem?
(CID:134686676)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 01:09 PM . Last Modified: β2024-04-04 12:38 AM
Hello Kris,
Due to you saying that the sensor is powering up, i am assuming that you are connecting an AP9520T or AP9520TH. These must be connected to the A-link ports, not a universal sensor port. The sensors ship with an invalid A-link address to prevent duplicate address on the A-link chain. The DIP switches must be adjusted for the sensor to work properly.
Kind Regards,
Cory
(CID:134686763)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 01:09 PM . Last Modified: β2024-04-04 12:38 AM
I am using the AP9520TH. I have had it connected to the A-link port but it doesnt show up. I have tried changing the address but that didnt seem to help. The other module I have tried in the universal ports is the AP9335TH. It works on a Netbotz 355 we have but not on this 570.
(CID:134688754)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 01:09 PM . Last Modified: β2024-04-04 12:38 AM
Kris Kincaide,
I recommend reaching out to your local technical support as there may be a hardware issue with the sensors or the NetBotz appliance itself.
Kind Regards,
Cory
(CID:134688756)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 01:09 PM . Last Modified: β2023-10-22 03:53 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.