DCE -EcoStruxure IT connection

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE -EcoStruxure IT connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

0 Likes
10
1254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

DCE -EcoStruxure IT connection

Hi

I want to know if DCE can still connect with StruxureOn (EcoStruxure IT) and availability  in LATAM region ( Costa Rica)

Thanks

Regards

(CID:134686600)

Labels
  • Labels:
  • Data Center Expert
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

0 Likes
6
1254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

Dear Sergio,

The information you need can be found on the official website https://ecostruxureit.com/ of this =SE= digital service.

At the moment, customers are already offered two digital services: EcoStruxure IT Expert (you can connect only the special free EcoStruxure IT Gateway software to it) and EcoStruxure Asset Advisor (you can connect your existing DCE software to it).

But unfortunately for both =SE= digital services in the section AVAILABLE IN your country is not declared (as well as mine :-). You need to wait...

With respect.

(CID:134686666)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

0 Likes
6
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

Dear Sergio,

The information you need can be found on the official website https://ecostruxureit.com/ of this =SE= digital service.

At the moment, customers are already offered two digital services: EcoStruxure IT Expert (you can connect only the special free EcoStruxure IT Gateway software to it) and EcoStruxure Asset Advisor (you can connect your existing DCE software to it).

But unfortunately for both =SE= digital services in the section AVAILABLE IN your country is not declared (as well as mine :-). You need to wait...

With respect.

(CID:134686666)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

ok, perfect, thanks for your information, butI am a little confused, it is a new service for which we must pay additional licenses and support?At this moment we are only interested in the mobile app connection with DCE,Maybe we don't have to wait too long
 
 

 

 

regards

(CID:134686672)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:07 PM . Last Modified: ‎2024-04-04 12:38 AM

Dear Sergio,

From your comment:

At this moment we are only interested in the mobile app connection with DCE,Maybe we don't have to wait too long

Then you only need =SE= digital service EcoStruxure Asset Advisor. How long will you have to wait I don’t know...

I am a little confused, it is a new service for which we must pay additional licenses and support?

You do not need additional licensing, but as written on resource https://ecostruxureit.com/how-to-buy/, you will need to pay an additional $365/USD/device/year.

More details about this and other questions regarding new digital services =SE= can be found in the recent topic .

If you have more questions, please ask.

With respect.

(CID:134686729)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

Hi,

Thanks for your answer

bad news for us, we think it's an expensive service. Today we have 150 devices (365*150=54750 USD per year) and we already pay for DCE: licenses, support contract, and APC-UPS support.

There is another way to obtain only the app working for our DCE?

 

With respect

(CID:134687476)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

Dear Sergio,

From your comments:

There is another way to obtain only the app working for our DCE?

Unfortunately, I don’t know another way for your case.

With respect.

(CID:134687486)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

ok , perfect  thanks for you time

 

Regards

(CID:134687493)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

Thanks for the feedback 😀.

(CID:134687498)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

0 Likes
1
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

Hi Sergio. 

May I jump in in the discussion

LATAM region will launch Asset Advisor in Dec 2018, so very soon. 

You can connect your DCE to the EcoStruxure IT cloud and then be connected to the Mobile App only, or to Asset Advisor or IT Expert.

If you are only interested in the Mobile App, you can connect and get the mobile App for free. You don't have to pay for the Mobile App. You will then be able to see Alarms and list of assets. 

By connecting, you will also get 30 days of free trial of IT Expert for all devices connected. You will see a lot of information in the Mobile App during the 30 days like Alarms, list of assets, and per asset list of sensors with history of values. After the 30 days period, you will have to decide to buy IT Expert or not. If you buy, you will continue to have the same views; If not, the mobile app will show you less information (alarms, list of assets)

By connecting, you can have 1 device covered by Asset Advisor for one year for free. For this device, you will see in the Mobile App a lot information (Alarms, Devices, Data history, Incidents, Chat with Service Bureau). You can have more devices connected to Asset Advisor but either buying it (365$/asset/year) or if you have a Service contract on some assets, these assets will be covered by Asset Advisor. For your assets covered by Asset Advisor, you will have a Service Bureau monitoring your assets, monitoring your incidents, chatting with you and calling you if necessary.

About your 150 devices, you can decide if you want all, or some of them covered to Asset Advisor. If some are covered by an Advantage Service Contract or Warranty, then they will be automatically upgraded to the full coverage. It's transparent for you, the system does it for you.

Hope it clarifies. Let me know

(CID:134688066)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

In response to DCIM_Support
0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2024-04-04 12:38 AM

Hi, Phillipe.

 

It is cristal clear to me now 😀.

 

thanks to everyone for your time and support.

(CID:134688095)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2023-10-22 01:16 AM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:08 PM . Last Modified: ‎2023-10-22 01:16 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore