Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-0407:50 PM. Last Modified: 2024-04-0411:05 PM
SNMP Device configuration Rack Manager
Hi Is it possible to migrate the Rack Access card details between the old PX-HiD kits and the new 250 because when I use device configuration template that contains the HiD card details this is not shown as an option??