EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 12:15 AM . Last Modified: ‎2024-04-05 04:39 AM
Humbly thankful for any assistance.
(CID:126160715)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 12:15 AM . Last Modified: ‎2024-04-05 04:39 AM
Hi Jared,
As spezialist suggested, the summary report will not show the time/date that the state was changed. To report this, you'll have to run a table report which will show the different states during the polling cycle. Although it may not be as exact as the event log, it will give you an idea of when it happened within a few minutes (polling cycle at most).
As for the zip file, again as spezialist noted we are currently unable to do this. It is by design however there is already an enhancement request ni the system for this. I will add a link to this post so that your info will be added to the existing request.
Thanks,
Steve
(CID:126162004)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 12:15 AM . Last Modified: ‎2024-04-05 04:39 AM
Hi jared reed,
Unfortunately, both your requests in the Schedule Data Export settings in the DCE-server can not be implemented. The only thing I can recommend in this case is to create a corresponding Feature Requests.
With respect.
(CID:126160843)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 12:15 AM . Last Modified: ‎2024-04-05 04:39 AM
Hi Jared,
As spezialist suggested, the summary report will not show the time/date that the state was changed. To report this, you'll have to run a table report which will show the different states during the polling cycle. Although it may not be as exact as the event log, it will give you an idea of when it happened within a few minutes (polling cycle at most).
As for the zip file, again as spezialist noted we are currently unable to do this. It is by design however there is already an enhancement request ni the system for this. I will add a link to this post so that your info will be added to the existing request.
Thanks,
Steve
(CID:126162004)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 12:15 AM . Last Modified: ‎2024-04-05 04:39 AM
Thank you Steve, this is a table report. All devices/sensors bar netbotz devices have this polling data. The netbotz devices only show the status at the time of the report.
Cheers for your help.
Jared
(CID:126162300)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 12:15 AM . Last Modified: ‎2023-10-22 03:46 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.