Hi,
I'm trying to collect SNMP traps from my Netbotz 250 NBRK0250. I found wired sensors data, but I can't find wireless sensor ones. I used bot netbotz454.mib and PowerNet-MIB.mib files, without any result.
Can anyone help me?
Thank you in advance,
Federico
(CID:128067110)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:11 AM . Last Modified: 2024-04-05 03:04 AM
Hi,
The NetBotz 250 is actually based on the APC Network Management Card and as such actually uses the APC "PowerNet.mib file located on the APC software downloads page:
Wireless temperature can be found using this OID:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.environmentalMonitor.envWireless.wirelessSensorStatus.wirelessSensorStatusTable.wirelessSensorStatusEntry.wirelessSensorStatusTemperature
.1.3.6.1.4.1.318.1.1.10.5.1.1.1.5
Steve
(CID:128067136)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:11 AM . Last Modified: 2023-10-22 03:17 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.