EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:41 PM . Last Modified: 2024-04-04 11:08 PM
Hello
Do you have some specification for air flow sensor in netbotz 155?
for example sensitivity of sensor and etc.
Thank you
(CID:132658922)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:41 PM . Last Modified: 2024-04-04 11:08 PM
Dear Aleksey,
Please check if the following k-base address your query.
http://www.apc.com/sy/en/faqs/FA158170/
Airflow sensor Range:
- 40 fpm to 400 fpm
Airflow sensor Accuracy:
+ or – 50 fpm
Regards,
Bala
(CID:132659063)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:41 PM . Last Modified: 2024-04-04 11:08 PM
Dear Aleksey,
Please check if the following k-base address your query.
http://www.apc.com/sy/en/faqs/FA158170/
Airflow sensor Range:
- 40 fpm to 400 fpm
Airflow sensor Accuracy:
+ or – 50 fpm
Regards,
Bala
(CID:132659063)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:42 PM . Last Modified: 2024-04-04 11:08 PM
Thank you
(CID:132660478)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:42 PM . Last Modified: 2023-10-22 03:15 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.