The device has stopped responding. When connected to the console, it displays:
Does not respond to keystrokes. This message is updated every 5-6 seconds. What can I do?
(CID:125209376)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 11:33 PM . Last Modified: β2024-04-05 04:53 AM
Hi Mukha,
Please check the reset button. We have seen a few instances where it was pushed in at an angle and got stuck. If that happens, it will continually reboot.
Steve
(CID:125209382)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 11:33 PM . Last Modified: β2024-04-05 04:53 AM
Thanks Steve, I checked the button. She's in a normal position.
(CID:125209502)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 11:33 PM . Last Modified: β2024-04-05 04:53 AM
Hi Mukha,,
That's about the only issue that I am aware of that would cause this. I'm assuming you've tried pushing it and centering it a few times.
If you've nothing connected to the unit and have tried another computer to be sure it's nothing about that system, it may be that an RMA is necessary. If you never get to the countdown to stop the boot "Does not respond to keystrokes" then there's no way to reflash.
Steve
(CID:125209579)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 11:33 PM . Last Modified: β2023-10-22 03:14 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.