NetBotz Rack Monitor 250 Firmware upgrade failed
Hello,
I have 3 NBRK-250 units installed at one of our client site.
We were facing an only problem that our TH sensors were showing only Temperature & Humidity values on NBRK-250 webpage, and no "Dew Point" values were found.
I have looked everywhere on its web interface but there's no clue regarding "Dew Point" values.
NBRK-250 manual says we need to upgrade its firmware.
A screenshot is attached for factory default firmware version:
I downloaded the latest available firmware at APC website:
Here's the log file from FW upgrade wizard:
Ping Test 07/30/19 11:17:43
-----------------
Ping Test 07/30/19 11:18:49
-----------------
[07/30/19 11:18:49] 192.168.0.64: Ping successful
Starting Upgrade 07/30/19 11:20:30
-----------------
[07/30/19 11:20:30] 192.168.0.64: Pinging (via ICMP) device
[07/30/19 11:20:30] 192.168.0.64: Device connection passed
[07/30/19 11:20:31] 192.168.0.64: Testing FTP Log-in
[07/30/19 11:20:34] 192.168.0.64: FTP Log-in passed
[07/30/19 11:20:35] 192.168.0.64: Saving data file
[07/30/19 11:20:39] 192.168.0.64: AOS Prior to firmware transfer: Network Management Card AOS v6.5.6
[07/30/19 11:20:39] 192.168.0.64: APP Prior to firmware transfer: NETBOTZ 250 APP v6.5.6
[07/30/19 11:20:39] 192.168.0.64: Saving event & configuration files
[07/30/19 11:21:06] 192.168.0.64: Transferring firmware file (1/3): Boot Monitor
[07/30/19 11:21:14] 192.168.0.64: Boot Monitor transfer successful
[07/30/19 11:21:16] 192.168.0.64: Restarting network interface
[07/30/19 11:29:38] 192.168.0.64: ERROR --> Device connection failed
Ping Test 07/30/19 11:30:43
-----------------
[07/30/19 11:30:44] 192.168.0.64: Ping failed
Ping Test 07/30/19 11:32:27
-----------------
[07/30/19 11:32:28] 192.168.0.64: Ping failed
************************************************************************
While upgrading, as you can see it kept working on the background for about 8 minutes & showed an error of device connection failed. My laptop was directly connected to the NBRK-250 & there's no connection error from my side.
Now its failing to ping and not even responding to Serial connection (Serial was working fine minutes before this upgrade).
if I try to reset it to factory defaults, the LEDs blink properly as if they're responding to the command.
But after over 2 hours, I can't be able to access it via network or serial connection.
Please tell me why Firmware upgrade created this issue.
And why my TH sensors are not showing Dew Point values by default.
Thanks in advance.
Raza Khan
(CID:147199923)
- Labels:
-
Data Center Expert
-
NetBotz
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:06 PM . Last Modified: 2024-04-03 12:59 AM
Hi Raza,
Good day!
The network connection may have been interrupted during the firmware update which is why it was not able to complete the file transfers.
To restore this, you may want to consider accessing the Netbotz 250's bootmon and follow the instructions from the article from the link below:
https://www.apc.com/au/en/faqs/index?page=content&id=FA293874
As for the "dew point" reading would you be able to identify what sensor did you add on the Netbotz 250 which led you to conclude that this reading should be available?
Edit: I visited the Netbotz appliances that we have here in our lab, and confirmed that Dew Point readings are only available with Netbotz devices 300, 400, and 500.
Dew point readings are not available in Netbotz 250.
Thanks.
Regards,
Justine
(CID:147199979)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:06 PM . Last Modified: 2024-04-03 12:59 AM
Dear Justin,
as I've mentioned before, my laptop was directly connected to NBRK250 & there's no chance of connectivity error but somehow it said there's a connection error.
And the link you provided is telling me about NMC recovery or upgrade not NetBotz device.
Please guide me how to recover NetBotz 250 device.
Regards,
M. Raza Khan
(CID:149291032)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2024-04-03 12:59 AM
Hi M. Raza Khan,
Thank you for your reply.
Unlike the other Netbotz appliances, the Netbotz 250 works the same as a typical NMC used in our Smart-UPS.
The set of instructions that I shared to you should apply to the Netbotz 250.
I hope this is clear.
Regards,
Justine
(CID:149291057)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2024-04-03 12:59 AM
Hi justin,
I've been trying serial with hyper terminal & puttry , its not even responding to serial connection.
is there any other way to access & restore this NBRK250 ?
or if you have any other tool to access & make it work, plz your urgent help is needed.
Regards,
M. Raza Khan
(CID:149291095)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2024-04-03 12:58 AM
Dear Raza Khan,
Please tell us, were you able to solve your problem or not?
With respect.
(CID:148771969)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2024-04-03 12:58 AM
No its not resolved yet.
kindly tell me how do I restore/recover it, as its not responding to ping or anything else.
Regards,
M. Raza Khan
(CID:149291026)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2024-04-03 12:58 AM
Dear Raza Khan,
Ok, did you try to restore the device via the COM port as Justine Chester pointed out to you?
With respect.
(CID:149291034)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2024-04-03 12:58 AM
Well its about recovering NMC but I tried, & its not even responding to serial connection.
Regards,
M. Raza Khan
(CID:149291054)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:07 PM . Last Modified: 2023-10-22 03:14 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.