Installing a temperature/humidity sensor with display (AP9520TH)
I am installing a temperature/humidity sensor with display (AP9520TH) to a NetBotz 250 (NBRK0250), but it is not showing up anywhere, I cannot find a way to configure it.
Thanks,
(CID:124526450)
- Labels:
-
NetBotz
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:12 PM . Last Modified: 2024-04-05 05:00 AM
Dear Sergio,
As stated in the installation manual, I would suggest you to make sure that you are using the CAT-5 straight through cable.
Normally, the sensor should show in the configuration page as shown below.
I am sharing some troubleshooting steps for this issue.
- Make sure that the power cable/ethernet/anything else are disconnected from the Netbotz 250 and that all Cat5 and terminators are disconnected from the AP9520TH sensors.
- There should be no physical connections at the Netbotz 250 (power/ethernet/anything) or the AP9520TH (Alink terminator).
- Once all are disconnected, set the dipswitches on each AP9520TH to off (Setting 1 - see below), and connect to the appliance. At this time, power on the Netbotz 250. When powered on, check if the sensor is recognized.
Regards,
Bala
(CID:124526568)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:12 PM . Last Modified: 2024-04-05 05:00 AM
Dear Sergio,
As stated in the installation manual, I would suggest you to make sure that you are using the CAT-5 straight through cable.
Normally, the sensor should show in the configuration page as shown below.
I am sharing some troubleshooting steps for this issue.
- Make sure that the power cable/ethernet/anything else are disconnected from the Netbotz 250 and that all Cat5 and terminators are disconnected from the AP9520TH sensors.
- There should be no physical connections at the Netbotz 250 (power/ethernet/anything) or the AP9520TH (Alink terminator).
- Once all are disconnected, set the dipswitches on each AP9520TH to off (Setting 1 - see below), and connect to the appliance. At this time, power on the Netbotz 250. When powered on, check if the sensor is recognized.
Regards,
Bala
(CID:124526568)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:12 PM . Last Modified: 2024-04-05 05:00 AM
Bala,
It is not showing in Configuration > Device > wired sensors, I am assuming that will be under Temperature & Humidity or since this is a A-link device should show in a different category? I can see the temperature in the device itself (display) but cannot see the device when I connect to the netBotz 250 via web or via Struxureware.
Let me know.
Thanks,
(CID:124527106)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:13 PM . Last Modified: 2024-04-05 05:00 AM
Bala,
I forgot to mentioned that if I connect the AP9335TH that came with the NetBotz 250, I can see the device right away, no problems with this one.
Thanks,
(CID:124527108)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:13 PM . Last Modified: 2024-04-05 05:00 AM
Hello,
The issue was resolved by correctly setting the DIP switch settings on the top of the sensor.
Best Regards,
Cory
(CID:124527110)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:13 PM . Last Modified: 2024-04-05 05:00 AM
Hi Sergio Garrido,
I am interested in your question, since I will soon have a similar task. Did you solve the problem according to the instructions below or not?
With respect.
(CID:124527423)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:13 PM . Last Modified: 2024-04-05 05:00 AM
Yes.... the instructions below are perfect.. my problem was that I was misinterpreting the settings in the DIP switch for the temperature/humidity sensor.
Thanks,
(CID:124527680)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:13 PM . Last Modified: 2024-04-05 05:00 AM
what did you do please? I had changed DIP Switch but I can't see any information in Netbotz
(CID:132647848)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:13 PM . Last Modified: 2023-10-22 02:46 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.