SSL Cert Import Issue - Not an X.509 Cert Error

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SSL Cert Import Issue - Not an X.509 Cert Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:13 PM . Last Modified: ‎2024-04-05 05:00 AM

0 Likes
6
3239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:13 PM . Last Modified: ‎2024-04-05 05:00 AM

SSL Cert Import Issue - Not an X.509 Cert Error

I am having trouble working with ssl certificates in the DCIM Portal.  I am receiving the following error when trying to import the cert.  keytool error:java.lang.Exception:  Input not an X.509 certificate.

(CID:124526883)

Labels
  • Labels:
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:13 PM . Last Modified: ‎2024-04-05 05:00 AM

0 Likes
0
3241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:13 PM . Last Modified: ‎2024-04-05 05:00 AM

Hi Krista Flynn,

Please share the command line and its output, that you are trying to import the Web Server SSL cert onto your SxW Portal. This will help to solve your problem faster.

With respect.

(CID:124526900)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

0 Likes
0
3242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

I generated the key request and send it to our CA with the following command. 

keytool -genkey -alias -keyalg RSA –keysize 2048 -keypass P@ssw0rd! -keystore .bin -storepass

keytool -certreq -keyalg RSA -alias -file certreq.csr -keystore .bin

I edited the /conf/server.xml file with the appropriate changes in the documentation.

Once I got the certs back from CA I tried to import with the following.  The second command below said it was successful.  The first command below I am getting the error above that I put in my question. 

  1. keytool -import -alias root -keystore mykeystore  -trustcacerts -file  chain_certificate_filename
  2. keytool -import -alias tomcat -keystore mykeystore -file certificate_filename


(CID:125208452)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

0 Likes
0
3242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

Once I got the certs back from CA I tried to import with the following. The second command below said it was successful. The first command below I am getting the error above that I put in my question.

1. keytool -import -alias root -keystore mykeystore -trustcacerts -file chain_certificate_filename
2. keytool -import -alias tomcat -keystore mykeystore -file certificate_filename

I.e., you can not perform the import the root CA cert? While the import the new SxW Portal Web Server SSL cert did you succeed? I understand you correctly?

If so, it's very possible that you are trying to import a file that is not a certificate. You can, for example, look at the properties of the chain_certificate_filename file on Windows to make sure that it is indeed a certificate file?

With respect.

(CID:125208454)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

0 Likes
0
3242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

Hi Krista Flynn,

In addition to the previous answer: to verify the validity of certificates, add to your files chain_certificate_filename and certificate_filename an extension, for example .cer: chain_certificate_filename.cer and certificate_filename.cer. Then, in the MS Windows environment, open the location of these two files by the explorer, you should see something similar with the indication that this is really a certificate:

Then just open (left-click on the file) first one file, and then another. If the file is indeed a digital certificate, you will see something similar with detailed information about the issuer of the certificate:


Otherwise, if the file is not a certificate file, you will get an opening error. This is an elementary test.

Always glad to answer your questions.

(CID:125208448)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

0 Likes
0
3242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2024-04-05 05:00 AM

Hi Krista Flynn,

Have you solved this problem or not?

With respect.

(CID:125208260)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2023-10-22 03:50 AM

0 Likes
0
3242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:14 PM . Last Modified: ‎2023-10-22 03:50 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore