Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:04 AM . Last Modified: 2024-04-08 11:08 PM
In DCE, how to configure the recipients of e-mail notification related to communication errors with NetBotz appliances?
It seems that by default, all users with a defined e-mail address receive the alert by e-mail and as I used remote users, their e-mail address are automatically imported from Active Directory
(CID:108825485)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:04 AM . Last Modified: 2024-04-08 11:08 PM
Hi Yannic,
Yes, that is the default behavior. If you check the release notes for 7.4 however:
You'll see that this function has been addressed:
Edit email address for remote users
You can now change the email address for LDAP and Active Directory users.
Steve
(CID:108825487)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:04 AM . Last Modified: 2024-04-08 11:08 PM
Hi Yannic,
Yes, that is the default behavior. If you check the release notes for 7.4 however:
You'll see that this function has been addressed:
Edit email address for remote users
You can now change the email address for LDAP and Active Directory users.
Steve
(CID:108825487)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:04 AM . Last Modified: 2024-04-08 11:08 PM
Hi Steve
Thanks for your answer and the reference to the last release note
I can see my question is in fact a Know Issue in DCE 7.3.1 and 7.4
"NetBotz Lost Communication Email Notifications are Sent to All Users"
It seems that unfortunately the Know issues are not indexed, I was not able to find it through the "Search" function of the help.se-dmaas.com
(CID:108825788)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:04 AM . Last Modified: 2024-04-08 11:08 PM
Hi Yannic, Yes, I had a hard time finding it too. Someone else also made note of that. I actually found it more easily on the release notes that were installed in the product. Either way though, 7.4 should be a resolution to your issue. Steve
(CID:108825789)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:05 AM . Last Modified: 2023-10-31 10:27 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.