EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:20 AM . Last Modified: β2024-04-08 11:22 PM
Is there anyway to delay the communication status alarm? At the moment there are a few devices that lose communication for a few minutes (a single poll cycle) then restore communication. This sets an alert for the loss then another alert for the restoration.
To conteract this I would like to set a threshold for a communication status alarm to only trigger after say 10 minutes.
(CID:108234558)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:20 AM . Last Modified: β2024-04-08 11:22 PM
You can set a delay for the alarm action to wait a certain amount of time before it will send a notification. In your case, you would want to set the delay to 10 minutes. If a device's communication is lost and restored in less than 10 minutes, notifications will not be sent.
Edit the properties of the notification policy which handles your communication threshold alarms. If using default settings, this will be your default notification policy.
Edit Notification Policy -> Edit Alarm Action
(CID:108234566)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:20 AM . Last Modified: β2024-04-08 11:22 PM
You can set a delay for the alarm action to wait a certain amount of time before it will send a notification. In your case, you would want to set the delay to 10 minutes. If a device's communication is lost and restored in less than 10 minutes, notifications will not be sent.
Edit the properties of the notification policy which handles your communication threshold alarms. If using default settings, this will be your default notification policy.
Edit Notification Policy -> Edit Alarm Action
(CID:108234566)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:20 AM . Last Modified: β2024-04-08 11:22 PM
Thanks Jesse, I'll put that into operation.
(CID:108234577)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:20 AM . Last Modified: β2023-10-31 10:26 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.