EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 10:45 PM . Last Modified: β2024-04-03 12:22 AM
Hello.
I am trying to use a NetBotz rack monitor NBRK0570 as Modbus slave and share temperature and humidity data to a Struxureware AS-P server via Modbus TCP for BMS applications.
I have enabled TCP/IP communication and generated Slave ID for rack and pods.
However, when I use a Modbus Scanner for to read the Modbus Map than NetBotz Advanced View gave me, all values I get are 57005 (0xDEAD).
Anyone know why I canΒ΄t get the correct values? Should I change another configuration, or something else? Or NetBotz is not useful for Modbus TCP communications if is not used with Data Expert?
Thank you!
(CID:149785217)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 10:45 PM . Last Modified: β2024-04-03 12:22 AM
Hi Gabriel,
I've enabled modbus over TCP on my 450. It's similar to the 570 but I didn't have anything connected to it for a quick test:
Then I set up the internal sensor pod as slave 1 and gave the few sensors registers:
Here are my settings using modbuspoll:
I'm getting responses. 0/1 are zero and 2/3 are zero because those are valid values for no smoke and off. 4/5 are 0 (less than 35565 on a 2x 16bit register) and 237 because 74.7 degrees in F is equal to 23.7 C.
The rest are -8531 (0xDEAD) because that is the output the bot gives if that register is invalid or disabled.
Perhaps you don't have the output enabled?
What version of firmware are you running? I'm at 4.6.4.
The rest is pretty simple, you appear to have the slave and register map configured...I can't speak about the BMS.
Steve
(CID:149785244)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 10:45 PM . Last Modified: β2024-04-03 12:22 AM
Hi Gabriel,
I've enabled modbus over TCP on my 450. It's similar to the 570 but I didn't have anything connected to it for a quick test:
Then I set up the internal sensor pod as slave 1 and gave the few sensors registers:
Here are my settings using modbuspoll:
I'm getting responses. 0/1 are zero and 2/3 are zero because those are valid values for no smoke and off. 4/5 are 0 (less than 35565 on a 2x 16bit register) and 237 because 74.7 degrees in F is equal to 23.7 C.
The rest are -8531 (0xDEAD) because that is the output the bot gives if that register is invalid or disabled.
Perhaps you don't have the output enabled?
What version of firmware are you running? I'm at 4.6.4.
The rest is pretty simple, you appear to have the slave and register map configured...I can't speak about the BMS.
Steve
(CID:149785244)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 10:45 PM . Last Modified: β2024-04-03 12:22 AM
Hi,
Try to read holding register 04 then address 31030? The modbus address should be 331030.
Best Regards,
TJ
(CID:149785387)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 10:45 PM . Last Modified: β2023-10-20 05:09 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.