Windows update KB5014692 seems to be causing Virtual ViewX to have login problems

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Windows update KB5014692 seems to be causing Virtual ViewX to have login problems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2022-06-22 12:46 PM . Last Modified: ‎2023-05-02 11:55 PM

0 Likes
9
4304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-22 12:46 PM . Last Modified: ‎2023-05-02 11:55 PM

Windows update KB5014692 seems to be causing Virtual ViewX to have login problems

I have a customer that is on Server 2019 and Geo SCADA 2020 December 2021 Update

and Virtual ViewX manager version 2.6.0.24

 

Sometimes they would get an error when logging in.

"Application Load Failed: Login Failure: the user has not been granted the requested logon type at this computer."

 

Not everyone is having the problem. Sometimes it works and sometimes it doesn’t. User1 can connect from one PC but not another. But User 2 CAN connect from a PC that won’t work for User1.

 

My customer found that the issue seems to be caused be by Windows Update “2022-06 Cumulative Update for Windows Server 2019 for x64-based Systems (KB5014692)”

That was the only change preceding the problems. Rolling back the update fixes the issues. It only is affecting the Virtual ViewX servers. The ViewX login on the Primary and Backup servers seem to be ok with the update applied (so far).

 

Seems others are having similar issues:

https://docs.microsoft.com/en-us/answers/questions/890250/kb5014692-jun-22-update-and-network-failur...

 

I have an email into support but just wanted to post this here now in case anyone else has this problem.

Labels
  • Labels:
  • Virtual ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-06-27 04:03 AM . Last Modified: ‎2022-10-19 12:46 AM

In response to sbeadle
1 Like
5
4195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-27 04:03 AM . Last Modified: ‎2022-10-19 12:46 AM

Thank you,

Notification added to Windows Updates testing page:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Microsoft-Update-Testing/ba-p/279120

Steve

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-10-17 01:08 AM

In response to Johnny07
1 Like
1
3521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-17 01:08 AM

Hi Johnny,

we are making good progress with the resolution. While we can't be sure about the release which will resolve it, it could be the one in November.

Our Beta release of Geo SCADA 2022 does have a fix for the issue, and also resolves compatibility with Windows Server 2022. If you wish to join the Beta programme and test this, please follow the directions at this posting:

https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/Geo-SCADA-2022-Beta-Testing-Would-you-like-...

(Note that there is a known issue with the Beta Virtual ViewX which causes context menu problems, but this is not connected to the Operating System issues).

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-01-04 01:17 AM

0 Likes
0
2992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-04 01:17 AM

The issue has been resolved and will require an upgrade of the Virtual ViewX Server using the December 2022 Update of Geo SCADA 2021. Find it at:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Geo-SCADA-Expert-Downloads/ba-p/279115

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-06-23 12:54 AM . Last Modified: ‎2022-10-19 12:47 AM

0 Likes
6
4274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-23 12:54 AM . Last Modified: ‎2022-10-19 12:47 AM

Thank you Geoff,

we have seen evidence of something similar and we are trying to understand this before notifying people on the Windows Updates testing page:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Microsoft-Update-Testing/ba-p/279120

Steve

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-06-27 04:03 AM . Last Modified: ‎2022-10-19 12:46 AM

In response to sbeadle
1 Like
5
4196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-27 04:03 AM . Last Modified: ‎2022-10-19 12:46 AM

Thank you,

Notification added to Windows Updates testing page:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Microsoft-Update-Testing/ba-p/279120

Steve

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

FilipZapletal
Crewman FilipZapletal
Crewman

Posted: ‎2022-09-18 12:23 AM

In response to sbeadle
0 Likes
4
3805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-18 12:23 AM

Hello,

 

I want to ask, if there is any progress or solution (other than dont installing updates) regarding this problem?

 

Our customers are asking us about this topic, because keeping their systems not updated is not acceptable in long term.

 

I was waiting for new monthly version release, but in release notes I have not found any mentions or further notes.

 

Thank you for answer.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-09-20 04:11 AM

In response to FilipZapletal
0 Likes
3
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-20 04:11 AM

Hi Filip,

Yes, the developers are making progress towards a solution. A beta is being trialled and has worked on 2022. There should be further news soon.

Thank you,

Steve

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Johnny07
Ensign Johnny07
Ensign

Posted: ‎2022-10-16 11:47 PM

In response to sbeadle
0 Likes
2
3527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-16 11:47 PM

Hello, is there any news about his issue?

 

Thanks,

 

Johnny

 

 

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-10-17 01:08 AM

In response to Johnny07
1 Like
1
3522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-17 01:08 AM

Hi Johnny,

we are making good progress with the resolution. While we can't be sure about the release which will resolve it, it could be the one in November.

Our Beta release of Geo SCADA 2022 does have a fix for the issue, and also resolves compatibility with Windows Server 2022. If you wish to join the Beta programme and test this, please follow the directions at this posting:

https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/Geo-SCADA-2022-Beta-Testing-Would-you-like-...

(Note that there is a known issue with the Beta Virtual ViewX which causes context menu problems, but this is not connected to the Operating System issues).

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Johnny07
Ensign Johnny07
Ensign

Posted: ‎2022-10-17 01:15 AM

In response to sbeadle
0 Likes
0
3512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-17 01:15 AM

Stephan, thanks for your quick response.

good to hear working on it and making progress.

 

Johnny

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

LeeAdvent
Crewman LeeAdvent
Crewman

Posted: ‎2023-01-03 01:15 PM

0 Likes
0
3018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-03 01:15 PM

Is there any update on this issue? 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-01-04 01:17 AM

0 Likes
0
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-04 01:17 AM

The issue has been resolved and will require an upgrade of the Virtual ViewX Server using the December 2022 Update of Geo SCADA 2021. Find it at:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Geo-SCADA-Expert-Downloads/ba-p/279115

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore