MOXA Nprot5630 After the GEO SCADA communication is configured, the content provided by the port log information
MOXA Nprot5630
After the GEO SCADA communication is configured, the content provided by the port log information
What is the reason that the virtual serial port data cannot be read? The serial port number is COM14 COM6
The contents of the port log are as follows
02-JUL-2023 08:50:46.248 [Main] Queuing Start MDRP Comms request for outstation "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Outstation" on current channel "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Channel"
02-JUL-2023 08:50:46.248 [Main] Sending Start MDRP Comms request (Id:2147483791) for "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Outstation" to "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Channel"
02-JUL-2023 08:50:46.248 [COM6] Adding Start MDRP Comms request to scanner COM6
02-JUL-2023 08:50:46.248 [COM6] Allow Start MDRP Comms request 30000 ms before timing out in scanner COM6
02-JUL-2023 08:50:46.248 [COM6] Activated Start MDRP Comms request for "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Outstation" in scanner COM6
02-JUL-2023 08:50:46.248 [COM6] Adding outstation "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Outstation" to scanner COM6 (Masters:1, Slaves:0)
02-JUL-2023 08:50:46.248 [COM6] Sending event Channel failed to "SPM_SCADA.MODBUS_rtu_TEST.New Group.New Direct Channel" from scanner
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-05 11:09 AM
This is most likely a problem with the Moxa configurations. You may be using the wrong driver from Moxa they have two this thread is about that.
In the Moxa configuration the ports have to be set to Real Com.
In the Moxa driver port configuration there is a setting that I forget what it is called but one option says something about Classic. I usually have to select that Classic option.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-05 11:09 AM
This is most likely a problem with the Moxa configurations. You may be using the wrong driver from Moxa they have two this thread is about that.
In the Moxa configuration the ports have to be set to Real Com.
In the Moxa driver port configuration there is a setting that I forget what it is called but one option says something about Classic. I usually have to select that Classic option.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-05 08:32 PM
The picture is to configure MOXA NProt configuration
Both driver and port mapping have been done
Both driver and port mapping have been done
problem still exists