Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

GeoSCADA Serial Write Fail with Moxa NPORT

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSCADA Serial Write Fail with Moxa NPORT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
103
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
SCADAPack 300E
product field
Schneider Electric
Trio Licensed Radios
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert
field url
Schneider Electric
SCADAPack 57x
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Teaan
Teaan
Troubleshooter

Posted: ‎2021-07-01 08:56 PM . Last Modified: ‎2023-05-03 12:02 AM

0 Likes
6
6707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 08:56 PM . Last Modified: ‎2023-05-03 12:02 AM

GeoSCADA Serial Write Fail with Moxa NPORT

Hi,

 

We needed to move one of our clients to a virtual enviroment after there GeoSCADA server failed, the original server connected to a Trio MR450 radio and Serial SMS modem. To interface to the serial devices now we have installed Moxa NPORT 5210 serial to ethernet devices and am using the REALCOM functionality on the server. 

 

Communicating using Trio Diagnostic software to the radios and with the SCADAPack's using the e-configurator.

 

However from GeoSCADA we almost get an immediate error that indicates channel failed, no Write in Progress. In the logs is returned as 0x40000011. This happens with all serial channels and almost happens immediately.

 

I have had this with support for more than a month now, without any resolution and have a very angry, irritated client on me. 

 

Does anybody know what this can be and have resolution for this?

 

Regards

Teaan

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
AndrewScott
Leader

Posted: ‎2021-07-02 02:50 AM

1 Like
4
6699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-02 02:50 AM

The Geo SCADA drivers use Windows overlapped I/O for asynchronous reads/writes to serial ports. The "No write in progress" errors means that the serial port device driver (Real COM) has signalled an asynchronous write has completed but no write is currently in progress, so this is unexpected.

 

This could be a fault with the Real COM device driver.

 

We've seen this same issue with Comtrol RocketPort and DeviceMaster serial ports. In this case the device driver signals each asynchronous write has completed twice - this is not standard behaviour for a serial port driver. Comtrol have a setting called 'Wait on physical transmission before completing write' which disables this non-standard behaviour. It might be worth asking Moxa if they have a similar feature in their Real COM device drivers.

 

A Geo SCADA driver log with the "I/O" and "Channels" logging options enabled showing the error occurring should confirm what is happening. This log will show each individual write start and complete.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Teaan
Teaan
Troubleshooter

Posted: ‎2021-07-02 06:08 AM

In response to AndrewScott
0 Likes
3
6696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-02 06:08 AM

Hi @AndrewScott ,

 

Thank you so much for your answer, it was indeed a driver issue. Moxa has two types of drivers it seems that one is driven through their Administrative suite software the other is Windows Drivers Manager. We only had the Administrative Suite installed and not the Windows Drivers Manager. We only had the the first mentioned installed, installing the second piece of software allowed the drivers to show up in the OS device manager and immediately everything started working.

 

Regards

Teaan

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
AndrewScott
AndrewScott
Leader

Posted: ‎2021-07-02 02:50 AM

1 Like
4
6700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-02 02:50 AM

The Geo SCADA drivers use Windows overlapped I/O for asynchronous reads/writes to serial ports. The "No write in progress" errors means that the serial port device driver (Real COM) has signalled an asynchronous write has completed but no write is currently in progress, so this is unexpected.

 

This could be a fault with the Real COM device driver.

 

We've seen this same issue with Comtrol RocketPort and DeviceMaster serial ports. In this case the device driver signals each asynchronous write has completed twice - this is not standard behaviour for a serial port driver. Comtrol have a setting called 'Wait on physical transmission before completing write' which disables this non-standard behaviour. It might be worth asking Moxa if they have a similar feature in their Real COM device drivers.

 

A Geo SCADA driver log with the "I/O" and "Channels" logging options enabled showing the error occurring should confirm what is happening. This log will show each individual write start and complete.


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Teaan
Teaan
Troubleshooter

Posted: ‎2021-07-02 06:08 AM

In response to AndrewScott
0 Likes
3
6697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-02 06:08 AM

Hi @AndrewScott ,

 

Thank you so much for your answer, it was indeed a driver issue. Moxa has two types of drivers it seems that one is driven through their Administrative suite software the other is Windows Drivers Manager. We only had the Administrative Suite installed and not the Windows Drivers Manager. We only had the the first mentioned installed, installing the second piece of software allowed the drivers to show up in the OS device manager and immediately everything started working.

 

Regards

Teaan

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Tyrone19
Tyrone19 Explorer
Explorer

Posted: ‎2021-08-10 05:54 AM

In response to Teaan
0 Likes
2
6597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-10 05:54 AM

Hi Teaan

 

How did you solve this? I am having the exact same problem now, ive installed both softwares however it still does not work.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Teaan
Teaan
Troubleshooter

Posted: ‎2021-08-11 08:26 AM

In response to Tyrone19
0 Likes
1
6587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-11 08:26 AM

Hi @Tyrone19 

 

You need to go to Program Files, under the moxa folder. There should be an application called Npcom, you need to open that and under advanced settings update it as shown in the picture below. This worked for me hope it helps you as well.

 

Capture.PNG

 

Regards

Teaan

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Tyrone19
Tyrone19 Explorer
Explorer

Posted: ‎2021-08-11 09:39 AM

In response to Teaan
0 Likes
0
6580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-11 09:39 AM

Hi 

 

Thank for this- It eventually did start working however there are time the modem loses coms but reconnects after a few seconds.

 

Thank you

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

文顶
文顶
Explorer

Posted: ‎2023-06-29 05:48 PM

0 Likes
0
4748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-29 05:48 PM

Geo SCADA communicates with Moxa serial port server because I have been unable to read the data of Moxa Nprot5630 here. How to set it up specifically, please show me

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore