Energy Hub IT firewall requirements

EcoStruxure Energy Hub

This forum is dedicated to supporting EcoStruxure Energy Hub service providers and partners with system implementation, reporting skills growth, and in demonstrating profitable improvements in monitored sites. Ask questions, get expert answers and the latest offer news, provide feedback and share community experience and knowledge!

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • EcoStruxure Energy Hub
  • Energy Hub IT firewall requirements
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thierry_Baudard
Commander Thierry_Baudard Commander
8
Mathew_Losey
Lt. Commander Mathew_Losey Lt. Commander
5
EduardoFainblum
Commander EduardoFainblum Commander
5
Marcus_Gasper
Commander Marcus_Gasper Commander
4
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Energy Hub
Start a Topic
Solved
Sandeep_EK99
Crewman Sandeep_EK99
Crewman

Posted: ‎2023-03-21 10:16 AM

0 Likes
1
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 10:16 AM

Energy Hub IT firewall requirements

Since Energy Hub is a cloud-based solution, what do I need to prepare with my client's IT? Do we need to open a specific port to allow connection to the cloud? We are going to be using a Panel Server that will connect through their local network.

Labels
  • Labels:
  • Knowledge Base
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Marcus_Gasper
Commander Marcus_Gasper Commander
Commander

Posted: ‎2023-03-21 11:08 AM . Last Modified: ‎2023-03-21 11:09 AM

1 Like
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 11:08 AM . Last Modified: ‎2023-03-21 11:09 AM

Hi Sandeep,
 
Panel Server needs an internet connection with access to the Schneider Electric cloud services to send measurement data to Energy Hub. Panel Server sends all the data over HTTPS and uses the same ports on the network firewall as standard web browsers. This makes Energy Hub easy to integrate into the IT network.
If the IT network uses a proxy server, then you need to configure the Panel Server proxy server settings.
If the network uses a firewall, then it needs to be configured to allow access to the Schneider Electric cloud services (also called endpoints).
 
You can find all this information and additional guidelines for network security in the Energy Hub IT and Security Guide.
 
Marcus Gasper
Technical Communicator

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Marcus_Gasper
Commander Marcus_Gasper Commander
Commander

Posted: ‎2023-03-21 11:08 AM . Last Modified: ‎2023-03-21 11:09 AM

1 Like
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 11:08 AM . Last Modified: ‎2023-03-21 11:09 AM

Hi Sandeep,
 
Panel Server needs an internet connection with access to the Schneider Electric cloud services to send measurement data to Energy Hub. Panel Server sends all the data over HTTPS and uses the same ports on the network firewall as standard web browsers. This makes Energy Hub easy to integrate into the IT network.
If the IT network uses a proxy server, then you need to configure the Panel Server proxy server settings.
If the network uses a firewall, then it needs to be configured to allow access to the Schneider Electric cloud services (also called endpoints).
 
You can find all this information and additional guidelines for network security in the Energy Hub IT and Security Guide.
 
Marcus Gasper
Technical Communicator
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.