Posted: 2024-12-22 06:52 AM
EEH Energy Calculation or day start time
Hi,
I need some help to configure EcoStruxure Energy hub.
1. i want to change day start time (e.g, from 6 AM) instead of default 00:00 AM.
2. how to configure Genset so that it will show as Generation not as consumption.
@Mathew_Losey could you please support.
Thanks
- Labels:
-
Knowledge Base
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-02 07:52 AM
1) Custom start times for days is not supported.
2) The genset usage should show energy as production not consumption. If you are seeing is as consumption you may need to set the "Meter wiring is reversed" setting in the info panel. By default energy delivered will be used for production, but depending on how the meter is installed production may be being recorded against the energy received measurement.