Network Management Card (AP9544) for Easy UPS 1-Phase Firmware v3.2.0.6 Release Notes

Easy UPS 1-Phase

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Network Management Cards
  • Network Management Card 3
  • Easy UPS 1-Phase
  • Network Management Card (AP9544) for Easy UPS 1-Phase Firmware v3.2.0.6 Release Notes
Options
  • Subscribe to RSS Feed
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

NMC Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Easy UPS 1-Phase
Options
  • Subscribe to RSS Feed
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
74 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Network Management Card (AP9544) for Easy UPS 1-Phase Firmware v3.2.0.6 Release Notes

Lieutenant SwathiNaidu Lieutenant
‎2025-03-26 03:21 AM

on ‎2025-03-26 03:21 AM

Affected Revision Levels

 

Component File Details
Easy UPS 1-Phase Application Windows:
snst_nmc3_eu1p_3-2-0-6.exe

Linux & macOS: 
snst_nmc3_eu1p_3-2-0-6.tar.gz

UPS Application for Easy UPS models SRV1KL-IN,

SRVPM3KRIL-IN, SRVPM2KRIL-IN, SRV1KUXI-IN,

SRV2KUXI-IN, SRV3KUXI-IN, SRV1KI, SRV2KI,

SRV3KI, SRVPM1KIL, SRVPM2KIL, SRVPM3KIL,

SRV1KRI, SRV2KRI, SRV3KRI, SRV2KL-IN,

SRV3KL-IN, SRV3KI-E, SRV1KRI-E, SRVPM1KRIL,

SRVPM2KRIL, SRVPM3KRIL, SRV1KA, SRV2KA,

SRV3KA, SRV1KRA, SRV2KRA, SRV3KRA,

SRVLPM1KRIL, SRVLPM2KRIL, SRVLPM3KRIL,

SRVSL1KRARK, SRVSL3KRARK, SRV2KRI-E,

SRVPM1KIL-E, SRVPM6KRI, SRVPM10KRI,

SRVPM10KIL, SRVSPM5KRI, SRV6KUXI-IN,

SRV6KL-IN, SRVSVPM5KRIL, SRVSL3KRIRK,

SRVLPM3KRIL-IN, SRVPM6KIL, SRVPM10KRIL-IN,

SRV10KUXI-IN, SRVLPM3KRIL-IN, SRVSL1KRIRK, SRVSL2KRIRK, SRVSL3KRIRK, SRVLPM6KRIL, SRV15KUXI-IN, SRV20KUXI-IN.

For details on upgrading the UPS Network Management Card (NMC) firmware, see the User Guide. 

 

New Features

 

New Feature

Support added for USB to Dry Contact Accessory for NMC (AP9811).
Security update
The customized .ini file name may optionally contain a CRC32 for integrity checking of the .ini file before processing.

 

Fixed Issues

 

Fixed Issue

The UPS fault alarm is now triggered only if there is a valid fault code received from UPS.

The External battery pack alarm text “battery pack X first level over voltage” is now changed to “Battery pack x full charged”.
Newly added External battery pack alarms are now translated to other languages such as Japanese, German, Chinese, French, Italian, Spanish, Portuguese, and Korean.
The first login banner message in NMC Web UI is now changed from "This Network Management Card includes a 12-month Support Contract. Firmware upgrades after this period will require an NMC Support Contract. See www.apc.com/upsnmc for more information" to "This Network Management Card includes a 1-year Secure NMC Subscription. Firmware upgrades after this period will require the purchase and activation of a new Secure NMC Subscription. Learn more at apc.com/secure-nmc"

The word site map is now correctly translated to the German language.

Fake alarm will not get logged when the configurations are changed through config.ini

Scheduled shutdown is now not triggered when Signal PowerChute Network Shutdown Clients is enabled.

When configuring a scheduled shutdown, now Signal PowerChute Network Shutdown Clients can be disabled and Turn Back On can be set immediately.

Security update

The following security vulnerability has been addressed in this release:

  • CWE-863: Incorrect Authorization.
The Network-Only user can only perform actions in the Web UI relevant to the user access level.

 

Known Issues

 

Known Issue

The Temperature and Humidity related information is displayed in the Help sections of CLI and Web UI, even though Temperature and Humidity sensors are not supported with AP9811. 

AP9811 'Output Relay 2’ parameter values can only be configured using Web UI and SNMP and not via CLI.

It is not recommended to change the Normal State of Input Contact from default Open state.

The firmware version and model number are not displayed in CLI when AP9811 is connected first time to NMC. It is recommended to disconnect and re-connect AP9811 to NMC in order to read the AP9811 firmware version and model number.

‘Put UPS in Bypass’ command is not available in the Device control commands of the I/O Contact Control Policy page.

Events related to Input dry contact and Output relay are displayed only in English language in all NMC interfaces.

AP9811 Input dry contact Events are not supported in PCNS.

The word “name” and “Vx-rail cluster shutdown error” is only available in English language.

“UPS: Deleted a One-Time scheduled shutdown” Event is not correctly translated in Japanese language.

Battery pack related events, "Battery pack x full charge" & "Battery pack x remains fully charged" are available only in English language.

Some unwanted characters are displayed when Event logs are viewed in French language.

Events are not logged for enabling and disabling of Bypass when UPS OFF & Bypass Not allowed configuration settings.

During Scheduled Shutdown of UPS, the graceful shutdown of UPS doesn't end at the configured time.

Note: This issue is specific to SRV15KUXI-IN.

Runtime Calibration does not perform as expected due to discrepancies between the Nominal battery voltage and the Rated battery voltage.

Note: This issue is specific to SRVSPM5KRI.

When the Runtime Calibration is performed for SRVPM6KRI unit, it does not undergo the Runtime Calibration and displays the critical alarm "The battery is not installed properly” even while the battery is connected.

 

Hash Signatures

 

Windows

Signatures

snst_nmc3_eu1p_3-2-0-6.exe

 CRC32

3F588000

CRC64

AD0520F85AD76058

SHA-256

1689AC882BAB5C99024A610FA2562B8118497A55F900AB149268F4E07DEEDC3A

SHA-1

94B3D99129A3E77A4CB65DC624DD541E0ABD0E5B

BLAKE2sp

E877411022DC1CA8E221BE46584E562DD89702321912DEE5942D9D64C4DA5F3E

 

Linux

Signatures

snst_nmc3_eu1p_3-2-0-6.tar.gz

 CRC32

EC5C51AD

CRC64

FED40CA6592A3B10

SHA-256

B58022A876B3BF70ECE7CF5CDABE231300C779A7E0C56AEDE52DBBE225AA9B8E

SHA-1

763ED22574B2B5424F7F53C57F64CBFA784A6430

BLAKE2sp

A1C9D29B15DA38FC470B8BAEC3B1A26052E7CBD8CEDA50E6107E454F2FAA2B70

 

macOS

Signatures

snst_nmc3_eu1p_3-2-0-6.tar.gz

 CRC32

05EF7DD0

CRC64

AE9A326DCB1BC6B1

SHA-256

CEC436153188615AE70281CF917AA3C57462CD27778FDF7742D24ECAB6E92AC7

SHA-1

4EEC3851883F3C25D696D2B9EB86B982BD910DFB

BLAKE2sp

26B263A2122EB86A564216C616D5A3080E36A50D0D677E8CBE21A3E9090DCAFE

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of