Network Management Card (AP9544) for Easy UPS 1-Phase Firmware v3.2.0.5 Release Notes

Easy UPS 1-Phase

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Network Management Cards
  • Network Management Card 3
  • Easy UPS 1-Phase
  • Network Management Card (AP9544) for Easy UPS 1-Phase Firmware v3.2.0.5 Release Notes
Options
  • Subscribe to RSS Feed
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

NMC Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Easy UPS 1-Phase
Options
  • Subscribe to RSS Feed
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
121 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Network Management Card (AP9544) for Easy UPS 1-Phase Firmware v3.2.0.5 Release Notes

Lieutenant SwathiNaidu Lieutenant
‎2025-03-17 04:57 AM

Affected Revision Levels

 

Component File Details
Easy UPS 1-Phase Application Windows:
snst_nmc3_eu1p_3-2-0-5.exe

Linux & macOS: 
snst_nmc3_eu1p_3-2-0-5.tar.gz

UPS Application for Easy UPS models SRV1KL-IN,

SRVPM3KRIL-IN, SRVPM2KRIL-IN, SRV1KUXI-IN,

SRV2KUXI-IN, SRV3KUXI-IN, SRV1KI, SRV2KI,

SRV3KI, SRVPM1KIL, SRVPM2KIL, SRVPM3KIL,

SRV1KRI, SRV2KRI, SRV3KRI, SRV2KL-IN,

SRV3KL-IN, SRV3KI-E, SRV1KRI-E, SRVPM1KRIL,

SRVPM2KRIL, SRVPM3KRIL, SRV1KA, SRV2KA,

SRV3KA, SRV1KRA, SRV2KRA, SRV3KRA,

SRVLPM1KRIL, SRVLPM2KRIL, SRVLPM3KRIL,

SRVSL1KRARK, SRVSL3KRARK, SRV2KRI-E,

SRVPM1KIL-E, SRVPM6KRI, SRVPM10KRI,

SRVPM10KIL, SRVSPM5KRI, SRV6KUXI-IN,

SRV6KL-IN, SRVSVPM5KRIL, SRVSL3KRIRK,

SRVLPM3KRIL-IN, SRVPM6KIL, SRVPM10KRIL-IN,

SRV10KUXI-IN, SRVLPM3KRIL-IN, SRVSL1KRIRK, SRVSL2KRIRK, SRVSL3KRIRK, SRVLPM6KRIL, SRV15KUXI-IN, SRV20KUXI-IN.

For details on upgrading the UPS Network Management Card (NMC) firmware, see the User Guide. 

 

New Features

 

New Feature

There is no new feature in this release.
Security update
The customized .ini file name may optionally contain a CRC32 for integrity checking of the .ini file before processing.

 

Fixed Issues

 

Fixed Issue

The UPS fault alarm is now triggered only if there is a valid fault code received from UPS.

The External battery pack alarm text “battery pack X first level over voltage” is now changed to “Battery pack x full charged”.
Newly added External battery pack alarms are now translated to other languages such as Japanese, German, Chinese, French, Italian, Spanish, Portuguese, and Korean.
The first login banner message in NMC Web UI is now changed from "This Network Management Card includes a 12-month Support Contract. Firmware upgrades after this period will require an NMC Support Contract. See www.apc.com/upsnmc for more information" to "This Network Management Card includes a 1-year Secure NMC Subscription. Firmware upgrades after this period will require the purchase and activation of a new Secure NMC Subscription. Learn more at apc.com/secure-nmc"

The word site map is now correctly translated to the German language.

Fake alarm will not get logged when the configurations are changed through config.ini

Scheduled shutdown is now not triggered when Signal PowerChute Network Shutdown Clients is enabled.

When configuring a scheduled shutdown, now Signal PowerChute Network Shutdown Clients can be disabled and Turn Back On can be set immediately.

Security update

The following security vulnerability has been addressed in this release:

  • CWE-863: Incorrect Authorization.
The Network-Only user can only perform actions in the Web UI relevant to the user access level.

 

Known Issues

 

Known Issue

The Temperature and Humidity related information is displayed in the Help sections of CLI and Web UI, even though Temperature and Humidity sensors are not supported with AP9811. 

AP9811 'Output Relay 2’ parameter values can only be configured using Web UI and SNMP and not via CLI.

It is not recommended to change the Normal State of Input Contact from default Open state.

The firmware version and model number are not displayed in CLI when AP9811 is connected first time to NMC. It is recommended to disconnect and re-connect AP9811 to NMC in order to read the AP9811 firmware version and model number.

‘Put UPS in Bypass’ command is not available in the Device control commands of the I/O Contact Control Policy page.

Events related to Input dry contact and Output relay are displayed only in English language in all NMC interfaces.

AP9811 Input dry contact Events are not supported in PCNS.

The word “name” and “Vx-rail cluster shutdown error” is only available in English language.

“UPS: Deleted a One-Time scheduled shutdown” Event is not correctly translated in Japanese language.

Battery pack related events, "Battery pack x full charge" & "Battery pack x remains fully charged" are available only in English language.

Some unwanted characters are displayed when Event logs are viewed in French language.

Events are not logged for enabling and disabling of Bypass when UPS OFF & Bypass Not allowed configuration settings.

During Scheduled Shutdown of UPS, the graceful shutdown of UPS doesn't end at the configured time.

Note: This issue is specific to SRV15KUXI-IN.

Runtime Calibration does not perform as expected due to discrepancies between the Nominal battery voltage and the Rated battery voltage.

Note: This issue is specific to SRVSPM5KRI.

When the Runtime Calibration is performed for SRVPM6KRI unit, it does not undergo the Runtime Calibration and displays the critical alarm "The battery is not installed properly” even while the battery is connected.

 

Hash Signatures

 

Windows

Signatures

snst_nmc3_eu1p_3-2-0-5.exe

 CRC32

075B1DF9

CRC64

AEB34FC8AF1752A4

SHA-256

02205291D43B8B0EDF5954EDB569E3E1D7152CC28441FB7D2A56C15E69410C01

SHA-1

18F8CCC1AE719F541C2BD1BF58FD689C5118D66A

BLAKE2sp

3176B6F01640873EEF862BD01CB268EBC60241E6D1325E205805C5EA4B7BC042

 

Linux

Signatures snst_nmc3_eu1p_3-2-0-5.tar.gz

CRC32

158AC146

CRC64

6C5AEF9DFB26D935

SHA-256

EC670AADB6E0BF507D9CCD325A0DF7CF4446C433C671DE3FC9137B98C0314F56

SHA-1

0388ECA2BE7DBF383834AFD746D845BF274A67D0

BLAKE2sp

D6D61730BFBF0B74699DCF673BC7736DBC3A53BA2CA4FD16543BC3606C505A97

 

macOS

Signatures snst_nmc3_eu1p_3-2-0-5.tar.gz

CRC32

009EBC1E

CRC64

9E892A4D4597E5F9

SHA-256

AC30AD4C4B5B251D841B5EB2DED7FBDBF8BE8AC101EE39AF7E0AF6DA554BB90E

SHA-1

E9C58BBE53DFC8A9D129E225B85291C120B0BA3E

BLAKE2sp

436C5CA893A6BFAB5555CC6FED9579931E02F199A7E3FBFB545638D35A7851D1

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of