Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Will IP settings persist when flashing a bCX4040 (BACnet) to a bCX9640 (Infinet)?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Will IP settings persist when flashing a bCX4040 (BACnet) to a bCX9640 (Infinet)?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • BillNeville
    BillNeville
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4124 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Will IP settings persist when flashing a bCX4040 (BACnet) to a bCX9640 (Infinet)?

Picard Product_Support
‎2018-09-10 06:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:08 PM

Issue

Do IP settings go to defaults when flashing from 4040 to 9640?

Product Line

Andover Continuum

Environment

  • bCX9640
  • bCX4040

Cause

Have a need to flash a controller from bCX4040 to bCX9640 over a remote connection access. Do not want to have to go to the site to reset IP settings. 

Resolution

Using CyberStation v1.93 a bCX4040 was flashed to a bCX 9640 and it did NOT lose its IP info.

Notes:

At the end of the upgrade an error was received: “The uprev could not communicate with the specified controller”. From the webpage it was noted that the IP address had not changed and the upgrade was successful.

It did not come back online in CyberStation. From the webpage, resetting it still did not bring it back online in CyberStation.

Changing the model number in CyberStation to bCX9640 (from bCX4040) to bring it back online was not an option.

The flash upgrade had reset the ACCNetID to 1.

The 4040 was then deleted (Bacnet side first then Infinity side) and a new 9640 was created. The proper ACCNetID was set up in the webpage and the changes committed. It was then online in CyberStation.

Bottom line – IP address never changed. ACCNetID did. The controller never had to be touched during this process so remotely doing this is expected to work. This was only tested using the latest firmware and CyberStation v1.93.

Of course, the best way to do this is on the bench not on a live system.

Please be aware that the model flash change will cause node count and/or xdriver upgrades to be reset if they were added as post-factory-shipment upgrades (via the Repair Dept) since these upgrade UPD files are model specific. See Node or XDriver Upgrade of BCX Inf (9640) to BCX BACnet (4040) or reverse.

Also see Update b3 or i2 OS, changing (converting) a controller, BACnet to Infinet or Infinet to BACnet .

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 7845
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore