Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Node or XDriver Upgrade of BCX Inf (9640) to BCX BACnet (4040) or reverse

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Node or XDriver Upgrade of BCX Inf (9640) to BCX BACnet (4040) or reverse
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Chris_Asbury
    Chris_Asbury
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2477 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Node or XDriver Upgrade of BCX Inf (9640) to BCX BACnet (4040) or reverse

Picard Product_Support
‎2018-09-06 12:41 PM

Issue

When upgrading a BCX Inf to BCX BACnet or vice versa , the BCX could lose any node count or X Drivers added using a post shipment factory *.upd cookies.

The settings return if the controller is flashed back to the original model type.

Product Line

Andover Continuum

Environment

  • Continuum 1.xx 2.xx
  • Windows
  • Infinet 
  • BACnet
  • Node Count, X Driver, X-Driver

Cause

This is because the cookie upgrade to add the node count (or other features) will be sent out for the format it is intended for, i.e. if the controller was BACnet then the file will be sent as BACnet, and if the controller was Infinet then the cookie will be Infinet

Resolution

New controllers shipped from the factory can be flashed either way between a 4040 and 9640 and it will not affect the settings for Node count, X Drivers or other options.

If a controller was to lose additional setting when it is convert from BACNet to Infinet or vice versa, there is a need to re-apply for the cookie upgrade file for the new model type. (it would of originally been ordered as additional options for the controller)

To re-apply for the cookie, contact your local repairs department with the controller details i.e serial number, controller type, etc, this will enable them to find your order and reissue the upgrade in the version it has been changed to.

Labels (1)
Labels:
  • Andover Continuum
Tags (4)
  • Find more articles tagged with:
  • 7304
  • comm
  • enabled
  • port
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of