Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Using BACnet IP to add a SmartStruxure Lite MPM to a StruxureWare Building Operation Enterprise Server or Automation Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using BACnet IP to add a SmartStruxure Lite MPM to a StruxureWare Building Operation Enterprise Server or Automation Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4412 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using BACnet IP to add a SmartStruxure Lite MPM to a StruxureWare Building Operation Enterprise Server or Automation Server

Product_Support
‎2018-09-11 06:07 AM

Last Updated: CraigEl Champion ‎2022-08-08 04:01 AM

Issue

Using BACnet IP to add a SmartStruxure Lite MPM to a StruxureWare Building Operation Enterprise Server or Automation Server

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation

Environment

StruxureWare Workstation

Cause

SmartStruxure Lite systems may desire an Enterprise Level Solution to bring multiple sites into one system.

Resolution

  1. Configure the SmartStruxure Lite MPM for BACnet IP as shown in MPM BACnet Integration.
  2. Ensure that the BACnet Network ID is Unique to the system and does not match the Network ID in use by the Enterprise Server
  3. Save the BACnet Configuration
  4. Be sure to Right Click on the Root Object of the MPM and save the database.
  5. Open StruxureWare for Building Operation Workstation
  6. Right Click on the Server Object and add a BACnet Interface
  7. Ensure that the BACnet interface has a unique BACnet Network ID which does not match the Network ID used by the MPM
  8. Expand the BACnet Interface
  9. Click on the Server Object and select the Device Discovery Tab
  10. Select BACnet Devices
  11. NOTE: There have been instances of Skype causing interference with this process. Please completely close Skype if you are using it and unable to discover any devices.
  12. ALSO NOTE: There may be 2 instances of the MPM shown. If so, use the MPM that is part of the Enterprise Server BACnet Network
  13. Drag the MPM to the BACnet Interface/IP Network object in the Enterprise Server System Tree
  14. Right Click on the Device and Upload it
  15. If any devices are connected to the MPM such as a Zigbee Wireless State or Enocean switch, these will be discovered in the BACnet Network configured in the MPM
  16. Add these devices to the Enterprise Server by dragging and dropping them to the BACnet Interface/IP Network object
  17. Right Click and upload all devices.
Labels (2)
Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 14310
  • issues
  • premium
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore