User access on a Reader Expander when in offline mode

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • User access on a Reader Expander when in offline mode
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele
  • JamesMorgan
    JamesMorgan
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • David_Kendrick
    David_Kendrick

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2662 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

User access on a Reader Expander when in offline mode

Picard Product_Support
‎2018-09-10 11:05 AM

Last Updated: Lieutenant JG JamesMorgan Lieutenant JG ‎2023-12-18 10:34 AM

Issue

  • Reader Expander loses communications to the SP-C, how are Users authenticated when they attempt to access Doors controlled from this Reader Module?
  • Which Users will still have access through Doors when the Reader Expander is offline to the (SP-C) Controller?

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert
  • SP-C
  • SP-RDM2

Cause

The SP-RDM2 Security Expert - Door Expansion Module - Installation Guide lists three options for how the SP-RDM2 should behave when it is offline from its SP-C controller.  The resolution below describes what each of these modes means.

Resolution

There are three options for how to handle access when the Reader Expander is in offline mode (not communicating with the Controller). 

1. No Users

Under Expanders | Reader Expander | General tab > Configuration section > Offline Operation, the “No Users” option removes access for any cards badged at these Readers. no one will have access while the Reader Expander is offline to the Controller.

No users.jpg

2. Any Card

Under Expanders | Reader Expander | General tab > Configuration section > Offline Operation, the “Any Card” option allows for any card at all to be granted access when the Reader Expander is offline to the Controller. This is the least secure option as anyone with a valid technology card, which is correctly formatted to either the Primary or Secondary formats defined for the Reader Expander, will be granted access.

  • There is no validation of the card's Facility Code or Card Number.
  • At present there is no option available for providing valid access on reading a card's Facility Code only.

any card.jpg

3. First 10 Users plus Cache

Under Expanders | Reader Expander | General tab > Configuration section > Offline Operation, the “First 10 Users plus Cache” option allows for the below Users to be granted access when the Reader Expander is offline to the Controller.

  • The first 35 Users in that Controllers Database.
  • The last 150 Users that have badged with valid access.

First 10-35.jpg

Note: This options text description is an old reference and will be updated in a new software version to reflect that this supports the first 35 Users.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (4)
  • Find more articles tagged with:
  • 19516
  • AdamSteele20
  • DavidKendrick20
  • JamesMorgan23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore