Upgrading Automation Servers from version 1.3 to 1.4

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading Automation Servers from version 1.3 to 1.4
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2515 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading Automation Servers from version 1.3 to 1.4

Picard Product_Support
‎2018-09-11 05:58 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:38 PM

Issue

When upgrading to 1.4, the reference system will be changed to follow newer more strict rules.

Product Line

EcoStruxure Building Operation

Environment

Device Administrator

Cause

With the release of 1.4, StruxureWare now has a tighter control on bindings. This is to prevent users from creating bindings which hinder system communication. When a system is upgraded from 1.3, to 1.4 any bindings that do not follow the new rule set will be dropped.

Here are the 3 major items for this new rule set. See Reference Guide and References beginning with 1.4.x for a full explanation.

  • Public Signal bindings will be dropped
  • Multiple bindings will be restricted to one
  • Bindings to Local Node NVIs will be dropped during the upgrade.

Resolution

To upgrade the Automation Servers, follow these steps:

NOTE: You will need to have a copy of Workstation at 1.3 in order to make changes to the Automation Server during the upgrade process. Use 1.4 Workstation after you have completed

  1. Perform a Manual Backup of the Automation Server. This backup must include historic data. Ensure that a copy of that backup is saved to an external disk as a recovery option.
  2. Open Device Administrator 1.4
  3. Connect to and Select an Automation Server
  4. Click Upgrade Device. Please Read the warning in this pop up message.
  5. This will upgrade the most recent backup of the Automation Server. Any changes to the system made since the last backup will be lost at the end of this process.

    Note that the yellow Progress bar means that you MUST review warning in the conversion log. If the progress bar is Yellow or Red, proceeding may result in irreversible system changes.
  6. Click "Open" under the conversion log column. This is very difficult to read in Notepad.
  7. Perform a Save as .txt and open this file in either Word Pad or NotePad++ for easier reading


    Notice the Change in display when the information is viewed in WordPad

  8. Use the notes from Reference Guide and References beginning with 1.4.x and the conversion log analysis from AS Conversion Log Analysis to make sure that all objects with WARNINGS meet the new rules. This will require making changes to the system via workstation.
  9. Repeat steps 1-8 until you are happy with the conversion log. Please note, that you must perform a new backup to get an updated log.
  10. Click on "Download updated database to devices"
  11. Click Okay in the pop up
  12. Wait for the Installation to finish successfully. If any errors occur, be sure to get a screen shot and contact Product Support

Note: If the upgrade doesn't complete correctly on one of the AS, cycle power on the AS, go back to the previous version and perform the upgrade again.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 14003
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore